Ray

Couple of thoughts on your application. We used to use the sunny islands a lot, challenge is they are only 120 volt so we needed to have two or add a transformer, which proved problematic with the grid tied inverters and hertz ranges.

So now we use the Outback 4048 and 8048 radians ( 8048 cost close to the same as a Sunny Island ) is 240, no transformer needed and a simple relay to break the main neutral on the enphases will shut them off when the voltage goes too high if the grid goes down and there is no load.

Outback also has their load center that has the circuitry built in to shut off the enphases. Keep it all ac, make it an AC coupled application, the enphases should work very well partnered with the radians. The radian hooks to the main service panel on AC in. AC out runs to the critical loads panel and you can run the enphase system right into the critical loads panel. While power is up the system works just like a grid tied system with the battery portion and radian in standby. When the power goes down, not a flinch, everything in the critical loads panel is hot, with the battery system and the grid tied system. Very nice setup

peter giroux
ASAE


----- Original Message ----- From: "Ray Walters" <[email protected]>
To: "RE-wrenches" <[email protected]>
Sent: Monday, August 17, 2015 4:10 PM
Subject: [RE-wrenches] AC Coupled with Generator


HI Esteemed Wrenches:

I am consulting on a system I have never seen, that consists of a 6.7Kw Enphase roof mounted system, and 2 backup generators. Each generator has an automatic 200 amp transfer switch to back up its own 200 amp panel. Both 200 amp panels are fed by a 400 amp service from the grid. The Enphase PV backfeeds a subpanel in another building which then is fed by a 2 pole 60 amp breaker in one of the 200 amp panels. Currently they are having issues with the generators kicking out because of the Enphase inverters. That part I understand: you can't backfeed a generator, or its voltage regulation freaks out.

Now we get to the fun part: they want to create a third critical load subpanel with loads selected from both 200 amp panels to be powered by batteries and an inverter. I am considering the Sunny Island since it makes the most sense with its ability to signal the Enphase inverters to shut off when the batteries are full. I also see this as a partial solution to the generator issue, since normally the Enphase will be connected to the output side of the Sunny Island. However, when the generator is used to charge, we will be back to directly coupling the generator output to the Enphase.

Here are some possible solutions I'm considering:
1) Use a separate charger for the generator so that it will only feed DC to the batteries, and not be AC coupled. 2) convert the PV back to DC with charge controllers, but that would involve ditching and adding another conduit run between buildings. 3) Put the Enphase PV on a relay that would disconnect the PV when charging with the generator. 4) Something I haven't thought of that one of you clever folks can suggest......

As always, thanks in advance for all you responses,

--
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to