Wrenches
The ability for proper charging has always been an issue way back befor ac 
coupling was a thing. Its near an uncontrolled charge and if you tank the 
batteries and shut down that's it no charging from the ac coupling component 
Jerry


Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone

<div>-------- Original message --------</div><div>From: Ray Walters 
<[email protected]> </div><div>Date:08/20/2015  6:56 PM  (GMT-10:00) 
</div><div>To: RE-wrenches <[email protected]> 
</div><div>Subject: Re: [RE-wrenches] AC Coupled with Generator </div><div>
</div>Hi Folks;

I've done more research on the whole AC coupled issue, and one flaw I found 
with both the Sunny Island and the Radian is that they can't really do a full 3 
stage charge for the batteries in off grid mode.
They detect that the batteries are full and disconnect the AC coupled GT 
inverters, but this is about as subtle as the very early charge controllers, 
and amounts to 1 stage charging.  This is fine for temporary outages, and when 
the grid comes back, the batteries get a good 3 stage charge.  But these folks 
are really wanting a design that could be taken off grid permanently.   Also as 
you my recall, the GT PV system is Enphase, so we can't use the more 
sophisticated controls that SMA offers for the Sunny boys. 
I hate to say it, but I might be back to a diversion load with PWM controller.  
Not elegant, but we could get 3 stage charging.  
Every time I look at AC coupled setups, I just want to start over with charge 
controllers. 
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760
On 8/17/2015 9:39 PM, Mac Lewis wrote:
Hi Ray,

With that size grid-tied system, you would want to use a battery based 
inverter(s) near the (6.7/0.8) 8000W range.  

The frequency shift of the Sunny Islands will work with kicking out the enphase 
inverters but you wouldn't get the same output ramping that it would offer if 
it was a Sunny Boy grid-tied inverter.  The Sunny Island can effectively solve 
your generator backfeeding because there is a reverse current sensor that will 
disconnect the AC input at whatever level you want, 50 mA is default I think.  
You may need to give the Sunny Island generator start control for this however.

You can read about it here on page 137.

http://files.sma.de/dl/15216/SI4548-6048-US-BE-en-21W.pdf

You'll need to give the Sunny Island a digital signal that tell it whether its 
connected to a generator or a grid as outlined in the manual. 

 This is where the Radian is nice because it has two AC Input terminals.

Sounds like an interesting project.

Good Luck.




On Mon, Aug 17, 2015 at 8:36 PM, Jerry Shafer <[email protected]> wrote:
I cant see this working well without some battery based inverter
Jerry

On Aug 17, 2015 10:10 AM, "Ray Walters" <[email protected]>                   
wrote:
HI Esteemed Wrenches:

I am consulting on a system I have never seen, that consists of a 6.7Kw Enphase 
roof mounted system, and 2 backup generators.  Each generator has an automatic 
200 amp transfer switch to back up its own 200 amp panel.  Both 200 amp panels 
are fed by a 400 amp service from the grid.
The Enphase PV backfeeds a subpanel in another building which then is fed by a 
2 pole 60 amp                     breaker in one of the 200 amp panels.
Currently they are having issues with the generators kicking out because of the 
Enphase inverters.  That part I understand: you can't backfeed a generator, or 
its voltage regulation freaks out.

Now we get to the fun part: they want to create a third critical load subpanel 
with loads selected from both 200 amp panels to be powered by batteries and an 
inverter.
I am considering the Sunny Island since it makes the most sense with its 
ability to signal the Enphase inverters to shut off when the batteries are 
full.  I also see this as a partial solution to the generator issue, since 
normally the Enphase will be connected to the output side of the Sunny Island.  
However, when the generator is used to charge, we will be back to directly 
coupling the generator output to the Enphase.

Here are some possible solutions I'm considering:
1) Use a separate charger for the generator so that it will only feed DC to the 
batteries, and not be AC coupled.
2) convert the PV back to DC with charge controllers, but that would involve 
ditching and adding another conduit run between buildings.
3)  Put the Enphase PV on a relay that would disconnect the PV when charging 
with the generator.
4) Something I haven't thought of that one of you clever folks can suggest......

As always, thanks in advance for all you responses,

-- 
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





-- 



Mac Lewis

"Yo solo sé que no sé nada." -Sócrates



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to