One way, if you want the feed to be on the customer’s side of the meter, is to 
install a new service panel with meter jaws that are designed to be “double 
lugged”. That is the two lugs on the customer side have accommodation for a 
solar backfeed. There are rules about the OCP and disconnect, but the entire 
arrangement is code compliant. 

 

Not every manu sells these panels, and off the top of my head I can’t remember 
the one we used many years ago. I’ll find out the make and model if you want.

 

-          Peter

 

Peter T. Parrish, Ph.D.

President, SolarGnosis

1107 Fair Oaks Ave.

Suite 351

South Pasadena, CA 91030

(323) 839-6108

[email protected]

NABCEP Certified PV Professional #031806-26

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of gary easton
Sent: Friday, September 25, 2015 6:11 AM
To: RE-wrenches
Subject: [RE-wrenches] large array on 200 amp service

 

Hello Wrenches,

What are folks doing when installing 100A plus of solar into a 200A service? 


 

-- 

Gary Easton
Appalachian Renewable Power

Stewart, Ohio 45778
NABCEP Certified Solar PV                                                       
     
T: 740-277-8498

 www.arp-solar.com

 


“First they ignore you. Then they laugh at you. Then they fight you. Then you 
win.”


~Ghandi

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org