One trick is to install an external meter base, so that you can use the 
original meter compartment for your supply side connection.  You'll also need 
jumper straps and a cover for the original meter base.

Nick Soleil
Enphase Energy
Cell: 707-321-2937

> On Sep 25, 2015, at 10:31 AM, Jason Szumlanski 
> <[email protected]> wrote:
> 
> Siemens makes a "Solar Ready" line. Whatever you plan to install, make sure 
> it's on the utility's list of approved devices. And...
> 
> Don't find out the hard way that your utility does not allow solar backfeed 
> directly to the double-lugs on the load side of the meter socket. It makes no 
> sense whatsoever, but we ran into one utility resisting our doing anything in 
> the meter can, claiming it was their domain until the conductors leave the 
> meter enclosure. The AHJ wasn't prepared to back us up. 
> 
> With a fusible disconnect immediately adjacent to the meter, you would think 
> this is the preferable interconnection method in every case from the 
> utility's perspective!
> 
> Jason
> 
> 
>> On Fri, Sep 25, 2015 at 11:15 AM, Peter Parrish 
>> <[email protected]> wrote:
>> One way, if you want the feed to be on the customer’s side of the meter, is 
>> to install a new service panel with meter jaws that are designed to be 
>> “double lugged”. That is the two lugs on the customer side have 
>> accommodation for a solar backfeed. There are rules about the OCP and 
>> disconnect, but the entire arrangement is code compliant.
>> 
>>  
>> 
>> Not every manu sells these panels, and off the top of my head I can’t 
>> remember the one we used many years ago. I’ll find out the make and model if 
>> you want.
>> 
>>  
>> 
>> -          Peter
>> 
>>  
>> 
>> Peter T. Parrish, Ph.D.
>> 
>> President, SolarGnosis
>> 
>> 1107 Fair Oaks Ave.
>> 
>> Suite 351
>> 
>> South Pasadena, CA 91030
>> 
>> (323) 839-6108
>> 
>> [email protected]
>> 
>> NABCEP Certified PV Professional #031806-26
>> 
>>  
>> 
>> From: RE-wrenches [mailto:[email protected]] On 
>> Behalf Of gary easton
>> Sent: Friday, September 25, 2015 6:11 AM
>> To: RE-wrenches
>> Subject: [RE-wrenches] large array on 200 amp service
>> 
>>  
>> 
>> Hello Wrenches,
>> 
>> What are folks doing when installing 100A plus of solar into a 200A service? 
>> 
>>  
>> 
>> --
>> 
>> Gary Easton
>> Appalachian Renewable Power
>> 
>> Stewart, Ohio 45778
>> NABCEP Certified Solar PV                                                    
>>         
>> T: 740-277-8498
>> 
>>  www.arp-solar.com
>> 
>>  
>> 
>> “First they ignore you. Then they laugh at you. Then they fight you. Then 
>> you win.”
>> ~Ghandi
>> 
>>  
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to