Wrencher's,
Quick question regarding sizing the fuse for a combined group of inverters.   
If I have six 10KW three phase inverters each with a max AC current of 30A they 
each require a 3 pole 40 A breaker.   If I then take the combined output of the 
AC combiner panel I see two possible options for sizing the combined fuse size. 
   

6 inverters x 40A breakers each = 240A so I need to use a 250A fuse
6 Inverters x 30A max output each = 180A x 1.25 = 225A Fuse

Seems like both are acceptable options since all wire will be protected.

All feedback is appreciated.
Al Frishman
AeonSolar

(917) 699-6641 - cell
(888) 460-2867
www.aeonsolar.com


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to