Hi Allen,

I always use the max output current method, not the fuse rating downstream.

Good Luck


On Sat, Oct 24, 2015 at 5:50 AM, Allen Frishman <[email protected]>
wrote:

> Wrencher's,
> Quick question regarding sizing the fuse for a combined group of
> inverters.   If I have six 10KW three phase inverters each with a max AC
> current of 30A they each require a 3 pole 40 A breaker.   If I then take
> the combined output of the AC combiner panel I see two possible options for
> sizing the combined fuse size.
>
> 6 inverters x 40A breakers each = 240A so I need to use a 250A fuse
> 6 Inverters x 30A max output each = 180A x 1.25 = 225A Fuse
>
> Seems like both are acceptable options since all wire will be protected.
>
> All feedback is appreciated.
>
> *Al Frishman*
> AeonSolar
>
> *(917) 699-6641 <%28917%29%20699-6641> - cell*
> *(888) 460-2867 <%28888%29%20460-2867>*
> *www.aeonsolar.com <http://www.aeonsolar.com/>*
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to