Two things, Combined OCPD sizing is based on the output current of the inverters, not the individual OCPD values. And in most 3 phase systems you will have a square root of 2 to factor into your calculations.
Sincerely, Glenn Burt Sent from my 'smart' phone so please excuse grammar and typos. -----Original Message----- From: "Allen Frishman" <[email protected]> Sent: 10/24/2015 7:50 To: "RE-wrenches" <[email protected]> Subject: [RE-wrenches] Combined Inverter Fuse sizing Wrencher's, Quick question regarding sizing the fuse for a combined group of inverters. If I have six 10KW three phase inverters each with a max AC current of 30A they each require a 3 pole 40 A breaker. If I then take the combined output of the AC combiner panel I see two possible options for sizing the combined fuse size. 6 inverters x 40A breakers each = 240A so I need to use a 250A fuse 6 Inverters x 30A max output each = 180A x 1.25 = 225A Fuse Seems like both are acceptable options since all wire will be protected. All feedback is appreciated. Al Frishman AeonSolar (917) 699-6641 - cell (888) 460-2867 www.aeonsolar.com
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org