Hi Daniel

Is this a new classic with OCP? Or maybe they don't have it anymore?

What it sure sounds like like is a big load on the batteries, it hits faster 
than the AGS can start, and the caps in the classic are dumping into the super 
low battery voltage. If this is happening in the AM, guessing with enough light 
to get the CC alive 

If there is a trimetric, you can measure the lowest voltage which should give 
you some good info. Super low volts might mean a bad battery or too big a load 
or both. 

But I don't believe it's the other way around that the classic is causing any 
issues with the AGS/inverter

You could always try another CC and see what happens

Jay

Peltz power
















> On Oct 26, 2015, at 6:30 PM, Daniel Tittmann <[email protected]> wrote:
> 
> Hive mind-
> hoping you all can help me solve this mystery issue.
> 
> System:
> Magnum double panel with Parallel stacked 2x4448 pae inverters.
> Classic 150 charge controller wired with an NMEPV 50 (din rail) and NMEPV100 
> 18 - 245 watt solar modules (6x3). (not over powered)
> 
> Issue:
> every morning the 100 amp din rail breaker is tripping.  from what I can 
> gather simultaneously the magnum RTR shows the AGS go into error.  Re set the 
> breaker and the solar works fine for the rest of the day.  
> 
> Not 100% sure the AGS has worked (under normal operation) at all other than 
> at commissioning and recent testing. 
> 
> Of course on site i cant get it to fail.
> 
> Tested the AGS by setting start voltage to 48.2 vdc and put the system under 
> load....... voltage drops and generator turned on with no pv-> Batt breaker 
> issue. 
> 
> last visit, chasing one theory, I re routed the battery + from the mnpv100 
> directly to the battery  + terminal as opposed to the battery + bus bar in 
> the inverter panel still didn't solve the problem.
> 
> I cant figure out if it the classic causing the issue or if it is the 
> inverters and the AGS.
> 
> Any input would be appreciated.
> Thanks
> Daniel
> 
> Daniel Tittmann 
> CTO
> Greenwired
> www.greenwired.com
> [email protected]
> 707-923-2001 (office)
> 707-206-5088 (Cell)
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to