Hi Daniel,

Do you know what the error is on the AGS? What are the start set points
that you have? Jay could be on to something if the battery voltage is
collapsing before the generator can start, the cc current could be high. Do
you know specifically what time of day the breaker is tripping?

I'd check the Midnite logs and consider starting the generator sooner.  Is
there large voltage swings (this could indicate bad battery or large load)?
Make sure the wire is cleaned and torqued properly onto that breaker.

How big is the battery bank and what is the tilt and azimuth of the panels?
On Oct 26, 2015 11:05 PM, "Jay" <[email protected]> wrote:

> Hi Daniel
>
> Is this a new classic with OCP? Or maybe they don't have it anymore?
>
> What it sure sounds like like is a big load on the batteries, it hits
> faster than the AGS can start, and the caps in the classic are dumping into
> the super low battery voltage. If this is happening in the AM, guessing
> with enough light to get the CC alive
>
> If there is a trimetric, you can measure the lowest voltage which should
> give you some good info. Super low volts might mean a bad battery or too
> big a load or both.
>
> But I don't believe it's the other way around that the classic is causing
> any issues with the AGS/inverter
>
> You could always try another CC and see what happens
>
> Jay
>
> Peltz power
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> On Oct 26, 2015, at 6:30 PM, Daniel Tittmann <[email protected]>
> wrote:
>
> Hive mind-
> hoping you all can help me solve this mystery issue.
>
> System:
> Magnum double panel with Parallel stacked 2x4448 pae inverters.
> Classic 150 charge controller wired with an NMEPV 50 (din rail) and
> NMEPV100
> 18 - 245 watt solar modules (6x3). (not over powered)
>
> Issue:
> every morning the 100 amp din rail breaker is tripping.  from what I can
> gather simultaneously the magnum RTR shows the AGS go into error.  Re set
> the breaker and the solar works fine for the rest of the day.
>
> Not 100% sure the AGS has worked (under normal operation) at all other
> than at commissioning and recent testing.
>
> Of course on site i cant get it to fail.
>
> Tested the AGS by setting start voltage to 48.2 vdc and put the system
> under load....... voltage drops and generator turned on with no pv-> Batt
> breaker issue.
>
> last visit, chasing one theory, I re routed the battery + from the mnpv100
> directly to the battery  + terminal as opposed to the battery + bus bar in
> the inverter panel still didn't solve the problem.
>
> I cant figure out if it the classic causing the issue or if it is the
> inverters and the AGS.
>
> Any input would be appreciated.
> Thanks
> Daniel
>
> Daniel Tittmann
> CTO
> Greenwired
> www.greenwired.com
> [email protected]
> 707-923-2001 (office)
> 707-206-5088 (Cell)
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to