Dan,
That problem of no AC at remote sites while waiting for replacement
batteries is why I always recommend at least two strings paralleled
through a buss bar rather than across terminals. That way if one
battery or cell fails in one series string you can very easily remove
the string from the buss without any AC downtime at all. It reduces
capacity but that's far better than no AC at all for a month. It's also
my firm belief that it extends battery life with that configuration.
I understand the thinking that drives the push to single string
installations but as someone who has lived off-grid for years in the
past redundancy was more important to me than the alleged "ease" of a
single string.
Tom
On 2015-12-15 11:04, Dan Fink wrote:
While I also advocate single strings and minimizing parallel strings
when off the grid, single strings have one big problem, especially in
more remote areas and especially with 6 volt batteries - 1-4 weeks
downtime of the whole AC side of the system while waiting for a
replacement battery and trying to receive and then deliver and install
it. During a blizzard, as always, of course. (got a doozy going on in
Colorado right here right now).
If there's a parallel string available, it's quick to rewire and
bypass a string with a bad battery in it temporarily . And if they are
2v cells and only one has failed, some quick inverter / charger / PV
controller reprogramming and bypassing that cell can quickly make a
functionable 22v /46v battery bank that will get your client by
until a replacement 2v cell arrives. Won't work on 12v, 10v is too low
for most every modern piece of equipment except DC loads.
Dan Fink
Adjunct Professor, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Accredited Continuing Education Providers™
970.672.4342 [11]
On Tue, Dec 15, 2015 at 11:08 AM, Howie Michaelson
<[email protected]> wrote:
While I have no experience with HUP, I do have many years of
experience with Rolls/Surrette. They are a robust battery, and in my
opinion superior to Trojan and other mid-line flavors. I am not as
adamant about staying away from L16s as Allan, although I'd
whole-heartedly agree with keeping to one string wherever possible,
and 2 at most.
Of course, going to the 2-volt batteries almost always allows for
single strings, and give you a much more robust battery, and are often
the right choice even for budget conscious clients. However, they are
a much larger investment and take a much more robust charging system.
Sometimes it makes sense to start a new off-gridder on a set of less
expensive "training" batteries, depending on your assessment of their
learning curve, motivation, and budget.
As with all batteries, there are occasional cell failures, likely
attributable to manu defects. But I've found with Rolls, this is less
common (except with the T12250 12-volt batteries which I have seen a
significant failure rate over with the years). And I have never had
trouble getting batteries covered under warranty from them if I
determine that the failure was not likely operator error. But this is
probably dependent upon having a good, trusting relationship with ones
supplier, which I've always had with RAE Battery.
Howie
HOWIE MICHAELSON
_NABCEP Certified Solar PV Installer™_
Sun Catcher, LLC
Renewable Energy Systems Sales and Service
VT Solar Electric Incentive Partner
802-272-0004 [10]
On Tue, Dec 15, 2015 at 12:37 PM, Allan Sindelar
<[email protected]> wrote:
Drake,
Your request is missing specifics so my answer can only be generic.
Get away from all L16s. Go to one string of industrial cells. There
are numerous well-respected brands. I would put HUPs at about the
top. www.hupsolarone.com [8]. Spend some time on this website and it
will become more clear.
Allan
ALLAN SINDELAR
[email protected]
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 [9] CELL
On 12/15/2015 9:07 AM, Drake wrote:
Hello Wrenches,
Even after my clients have learned to maintain their batteries
properly, the Trojan L-16 batteries continue to crater, one cell at
a time. One client is considering spending $12,000 on a nickel -
iron battery bank he found on the web. This seems like a
ridiculously large investment, but he is feeling desperate. We
urgently need another option from the Trojan L-16s.
How are the Surrette L-16s holding up? Would you recommend them as
worth the extra investment?
What is the best battery to use in an off grid system these days.
Thanks,
Drake
Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328 [5]
http://athens-electric.com/ [6]
[7]
This email has been sent from a virus-free computer protected by
Avast.
www.avast.com [7]
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[1]
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
[2]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [3]
Check out or update participant bios:
www.members.re-wrenches.org [4]
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[1]
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
[2]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [3]
Check out or update participant bios:
www.members.re-wrenches.org [4]
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[1]
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
[2]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [3]
Check out or update participant bios:
www.members.re-wrenches.org [4]
Links:
------
[1]
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
[2]
http://www.mail-archive.com/[email protected]/maillist.html
[3] http://www.re-wrenches.org/etiquette.htm
[4] http://www.members.re-wrenches.org
[5] tel:740-448-7328
[6] http://athens-electric.com/
[7]
https://www.avast.com/?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient
[8] http://www.hupsolarone.com
[9] tel:505%20780-2738
[10] tel:802-272-0004
[11] tel:970.672.4342
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org