Hi Gregory
If your installing a new load center
Try inserting a 2" "C" condulet
Ahead of the service panel
I'm assuming pvc conduit from meter to panel
Install solid core 200:5 ct's while you pull your cable through
Route the ct leads into the panel along with the phase conductors
Or if you have a meter main
Most have bolted buss connections that you can open and if you stagger the ct's 
and support them with a few cable ties
That could work
But
Your meter probably requires voltage sense and meter power conductors so 
nippling the meter to the panel might be a better solution just so you don't 
have to install additional oc protection in the meter main
Which might be sketchy
Hope I understood your question
Pat

Patrick A. Shortell
Licensed Master Electrician
Certified Solar Installer
71 Oregon Street
Long Beach N.Y. 11561
Www.thesolarstorehouse.com


> On Feb 17, 2016, at 2:29 PM, jerrysgarage01 <[email protected]> wrote:
> 
> Can you get a meter main with only one breaker and then get a distribution 
> panel and put all all loads there
> 
> 
> Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
> 
> 
> -------- Original message --------
> From: Gregory Seelhorst
> Date:02/17/2016 6:23 AM (GMT-10:00)
> To: RE-wrenches
> Subject: [RE-wrenches] Optimal 200 or 225 Amp Square D MSP All-in-One meter   
> for CT Clamps
> 
> Wrenches -
> 
> Does anyone know of a good spec for a 200 or 225A Square D Main Service Panel 
> which has feeders between the meter and Main Disconnect and would be ideal 
> for 150A CT clamps for monitoring whole house consumption?
> 
> I'm finding most MSPs have a short, flat bus between the meter and Main 
> Disconnect which requires the Rigowski Coil (requiring more expensive and 
> unreliable hardware).
> 
> Thank you for your help in advance.
> 
> Regards,
> 
> Greg Seelhorst
> NABCEP PV Installation Professional #092907-16
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org