Solmetric has some good screen shots of what happens when you combine these 
modules. My students just did a lab of combining modules (210W and 175W) in 
series and parallel and testing the PVA 600.  In series V add and current drags 
way down to the lowest I value in the series string. The IV curve looks so 
screwy that a MPPT will have a very hard time locating the  MPP. In parallel 
the IV curve looks much more stable. Parralel would be the best way to combine 
different modules. 
I can send some photos of the IV curves if you'd like. 
Jesse Dahl

NABCEP PV Installation Professional
IBEW Local 292 - Electrician 
Electrical/Solar PV Instructor - HCC

Sent from my iPhone

> On Jun 23, 2016, at 1:17 AM, Dan Fink <[email protected]> wrote:
> 
> Dan; rough-and-tumble world indeed here off the grid! My understanding is 
> that Voc will still be additive, minus degradation over the years, but that 
> the larger Pmax modules will be current limited for Imp by the smaller ones. 
> So your 245w modules could only do 100w in the scenario you give.
> 
> My solution has always been just stick with PWM controllers in these 
> situations.
> 
>> On Jun 22, 2016 10:37 AM, "Daniel Tittmann" <[email protected]> wrote:
>> In the rough and tumble world of off grid system management for people who 
>> have been piecing together systems for years it is not uncommon for our 
>> company to come to a project and find many different types of solar modules. 
>>  In most cases these modules are working fine and producing power but often 
>> have different output profiles.   In an effort to upgrade systems and 
>> increase production I have often had the idea of building string of these 
>> different modules and feeding them into an MPPT controller. 
>> 
>> Can anyone out there explain if this would be a good idea or a bad one? 
>> 
>> Let say we have 
>> 4 x 100 watt 17.5 Vmp modules 
>> 2 x 245 watt 30.5 Vmp modules
>> 
>> what would be the outcome of 2 strings of modules
>> both with: 2 x 100 watt + 1 x 245 watt  
>> would this cause issues with the MPPT controller (say OB FM60) or the 
>> modules? Obviously you need to build strings that will fit the profile of 
>> the controller and not over to the series string rating and voltage 
>> tolerance of the modules but from a production standpoint where does this 
>> land?
>> 
>> thanks for your advice
>> Cheers-
>> Daniel
>> 
>> 
>> 
>> Daniel Tittmann 
>> CTO
>> Greenwired
>> www.greenwired.com
>> [email protected]
>> 707-923-2001 (office)
>> 707-206-5088 (Cell)
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to