I am working with a customer who is doing a complete remodel, and upgrading to 
PV and Smart Energy Storage. The house was broken down to floor joists, open 
studded walls and open roof rafters.

 

The client wanted a 8 kW/16 kWh Smart Energy Storage system and a 10 kW-ac PV 
system. The Main panel, the Critical Load sub-panel, the Energy Storage system 
and the PV inverters will all be either in a detached garage or hung on the 
west facing exterior wall of the detached garage.

 

We have been given a number of 1-1/2” PVC conduits, buried a minimum of 18”,  
that run between the main house and the detached garage, so we have to convey 
2/3rds of the PV source circuits and all of the critical load branch circuits 
using this conduit. This raises a number of questions/confirmations:

 

(1)    We cannot mix PV source circuits and critical load branch circuits in 
the same conduit. Pretty obvious.



(2)    What ambient temperature should I use in my ampacity calculations? I 
assumed something less than 30°C, such as 20°C. But I read somewhere that one 
has to be careful when the conduit exists the ground, in that one has only 18” 
of conduit above ground before one has to use the full maximum ambient 
temperature which in our case is 45°. The argument says that for the first 18”, 
the portion of the copper conductors in the ground will cool the portion of the 
conductors above ground via thermal conduction. I can’t find any citation to 
confirm this argument. Does anyone have any sources of information on the 
subject? Even if there is a sound engineering basis for the argument, soon 
after exiting the ground, one would need a vault to splice in a higher ampacity 
conductors and continue on to either the critical load sub-panel or the 
inverters, you have to calculate the ampacity at 45°C. These buried conduit 
runs are approximately 50 feet in length.



(3)    One end of the conduit run is supposed to come out of the ground inside 
the building envelope, so we could derate using 30°C or so for air conditioned 
space. We cannot count on the garage being air conditioned however.



(4)    Can we use THHN as opposed to THWN-2? I am assuming the forces of nature 
or human stupidity will eventually cause the PVC to crack and the extra expense 
of THWN-2 (or another wet rated 90°C  conductor) will be a better choice.

 

This job is the same one where the electrician claimed that neutrals on a 120V 
branch circuit don’t count as current carry conductors in conduit for the 
purposes of de-rating ampacity. He’s gone, but his replacement may not be any 
more careful in his ampacity calculations.

 

Faithfully yours,

 

Peter T. Parrish, Ph.D.

NABCEP™ Solar Professional #031806-26

President, SolarGnosis

1107 Fair Oaks Ave.

Suite 351

South Pasadena, CA 91030

(323) 839-6108

[email protected]

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to