I don't know what they're listed for but I know that they are very effective.

Michael D Nelson
MD Electric & Solar, Inc.
707-684-0064 mobile
707-884-1862 office
www.mdelectricsolar.com
Sent from my iPhone

> On Aug 10, 2016, at 2:51 PM, Glenn Burt <[email protected]> wrote:
> 
> But are they listed to be used with greater stranded conductors than class B 
> or C (7 or19)?
> From: Carl Adams
> Sent: ‎8/‎10/‎2016 17:37
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
> 
> I second Mike Nelson's approach, simple, easily inspectable, rugged.
> 
> Carl Adams
> SunRock Solar
> NABCEP Certified PV Installer
> 
> 
>> On Aug 10, 2016 12:20 PM, "Mike Nelson" <[email protected]> wrote:
>> I have been using buchannon copper crimps with their plastic snap on "wire 
>> nuts" for years to splice rooftop wires (enphase or pv wire to string 
>> inverter) inside junction boxes or soladecks. Best connection you can have 
>> and I've never had one come loose or melt down.
>> 
>> Michael D Nelson
>> MD Electric & Solar, Inc.
>> 707-684-0064 mobile
>> 707-884-1862 office
>> www.mdelectricsolar.com
>> Sent from my iPhone
>> 
>>> On Aug 9, 2016, at 11:03 PM, Ray Walters <[email protected]> wrote:
>>> 
>>> I think the issue has always been locating the right parts, not the 
>>> installation.  Everyone carries the Cobra X flex, but not the ferrules. We 
>>> usually crimp lugs on and use breakers with stud terminals, so the need for 
>>> ferrules is minimal. 
>>>  I have always wondered about the terminal bussbars from Outback and 
>>> Midnite though.  They're ILSCO and I can't find any mention about extra 
>>> flex, which usually means they are not rated for anything beyond Class B 
>>> stranding.
>>> 
>>> R.Ray Walters
>>> CTO, Solarray, Inc
>>> Nabcep Certified PV Installer, 
>>> Licensed Master Electrician
>>> Solar Design Engineer
>>> 303 505-8760
>>>> On 8/8/2016 9:54 PM, Jay wrote:
>>>> Thimbles are easy to install and make fine strand wire OK for use in 
>>>> standard connections. 
>>>> 
>>>> Jay
>>>> Peltz power. 
>>>> 
>>>> On Aug 8, 2016, at 5:39 PM, Glenn Burt <[email protected]> wrote:
>>>> 
>>>>> Be aware that depending upon the vintage of the Engage cable, up to 
>>>>> recently the conductors used in their cables are fine stranded and cannot 
>>>>> be used in the terminal blocks provided with the Soladeck. 
>>>>> This has been acknowledged by Enphase with a revision to
> 
> [The entire original message is not included.]
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to