Well, I did a little research on these crimps, and they are definitely not 
listed for use with anything other than class B or C stranding.

So although that may be  the way someone has done it all the time, that is not 
a defensible argument when it comes to a code violation.

 

Buchanan-Ideal Splice Cap

UL listing E5238

UL 486C

 

UL certificate ZMVV.E5238 

This standard clearly defines Class C or B stranding as acceptable

The UL 486C standard also describes their use only for Class B or C stranded 
conductors

 

NEC 2014

Article 110.14 Electrical Connections

‘Connectors and terminals for conductors more finely

stranded than Class B and Class C stranding as shown in Chapter

9, Table 10, shall be identified for the specific conductor

class or classes.’

 

So if you are using the older style Engage cables (TC-ER 12 AWG fine stranded 
cables), you must source appropriate (read listed for this use) connectors.

 

Researching appropriate methods and techniques as well as continual education 
makes us all better installers. Codes and materials are dynamic in nature and 
it is up to us to constantly be on guard for changes that affect the safety and 
reliability of the systems we install. 

 

Manufacturers are not always correct! Simply because a manufacturer say to ‘do 
it this way’ does not mean we should ignore the NEC.

 

I identified the same issue with a dual axis tracking manufacturer recently 
that supplied SO cord for flexibility and standard Square D circuit 
breakers/panelboards as connection points. These also were connected together 
in violation of the breaker/panel listing and they told me they are making a 
change to supply appropriate ferrules to be used.

 

From: RE-wrenches [mailto:[email protected]] On Behalf 
Of Mike Nelson
Sent: Wednesday, August 10, 2016 7:07 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase

 

I don't know what they're listed for but I know that they are very effective.

Michael D Nelson

MD Electric & Solar, Inc.

707-684-0064 mobile

707-884-1862 office

www.mdelectricsolar.com

Sent from my iPhone


On Aug 10, 2016, at 2:51 PM, Glenn Burt <[email protected]> wrote:

But are they listed to be used with greater stranded conductors than class B or 
C (7 or19)?

  _____  

From: Carl Adams <mailto:[email protected]> 
Sent: ‎8/‎10/‎2016 17:37
To: RE-wrenches <mailto:[email protected]> 
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase

I second Mike Nelson's approach, simple, easily inspectable, rugged.

Carl Adams
SunRock Solar
NABCEP Certified PV Installer

 

On Aug 10, 2016 12:20 PM, "Mike Nelson" <[email protected]> wrote:

I have been using buchannon copper crimps with their plastic snap on "wire 
nuts" for years to splice rooftop wires (enphase or pv wire to string inverter) 
inside junction boxes or soladecks. Best connection you can have and I've never 
had one come loose or melt down.

Michael D Nelson

MD Electric & Solar, Inc.

707-684-0064 mobile

707-884-1862 office

www.mdelectricsolar.com

Sent from my iPhone


On Aug 9, 2016, at 11:03 PM, Ray Walters <[email protected]> wrote:

I think the issue has always been locating the right parts, not the 
installation.  Everyone carries the Cobra X flex, but not the ferrules. We 
usually crimp lugs on and use breakers with stud terminals, so the need for 
ferrules is minimal. 
 I have always wondered about the terminal bussbars from Outback and Midnite 
though.  They're ILSCO and I can't find any mention about extra flex, which 
usually means they are not rated for anything beyond Class B stranding.




R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760 <tel:303%20505-8760> 

On 8/8/2016 9:54 PM, Jay wrote:

Thimbles are easy to install and make fine strand wire OK for use in standard 
connections. 

 

Jay

Peltz power. 


On Aug 8, 2016, at 5:39 PM, Glenn Burt <[email protected]> wrote:

Be aware that depending upon the vintage of the Engage cable, up to recently 
the conductors used in their cables are fine stranded and cannot be used in the 
terminal blocks provided with the Soladeck. 
This has been acknowledged by Enphase with a revision to 

 

[The entire original message is not included.]

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to