So this may be a dumb question, but I'm assuming wire nuts are not suitable for Fine strand wire? I agree that most installs are not code compliant in this regard. Its really tough to find parts or even good info on this.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 8/11/2016 8:03 AM, August Goers wrote:

Hopefully manufacturers will steer away from supplying fine stranded wires with their trunk cables – it’s been a joke trying to fine the proper listed reasonably priced parts to make these connections. I bet that a huge percentage of the installs out there are not meeting the listing for fine stranded conductors.

That said, we use ferrules on the individual fine stranded conductors and then make the splices with the Ideal/Buchanan splice caps. This particular combo was presented in the SunPower ACPV instruction document and says it is listed for their class K conductors. I haven’t looked up the listing documents myself (at least recently) since this was presented in the manufacturer’s manual. As I posted before, the Ideal splice caps are the bomb! We love them and I’d highly recommend checking them out if you haven’t already.

Best,

August

Luminalt

*From:*RE-wrenches [mailto:[email protected] <mailto:[email protected]>] *On Behalf Of *Glenn Burt
*Sent:* Wednesday, August 10, 2016 8:44 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Pass through/transition box for Enphase

The Ideal website for the Buchanan splice has a link to the UL listing for the product. It does not list it for use with anything other than standard stranded conductors. If it is not part of the listing, it is not approved for that use, regardless of historical or anecdotal use. That is what the NEC says, and what the UL listing says and the UL specification for their listing says.

------------------------------------------------------------------------

*From: *Brian Teitelbaum <mailto:[email protected]>
*Sent: *‎8/‎10/‎2016 22:48
*To: *RE-wrenches <mailto:[email protected]>
*Subject: *Re: [RE-wrenches] Pass through/transition box for Enphase

Jeremy,

Without digging into the specs on the Ideal connectors, I doubt that they will work with fine-stranded wire.

The problem with these types of connectors is that the set screw that you turn to tighten the connection is in direct contact with the wire strands. As you tighten it, it rubs the strands in a circular motion, which will stretch, flatten, and tear the strands. It would work fine if you use ferrules, but not without them.

Terminals that are rated for direct use with fine-stranded wire would have a clamping-type terminal, where the screw used to tighten the connection pushes down on a solid piece of metal which then clamps the wire. Even in this case, it may still not be approved for fine-stranded wire depending on its design.

The Buchanan splices should be fine. They are basically the same as a ferrule, except that they are crimped with a crimping tool instead of the pressure from tightening a screw in a bus bar. The crimping tool is not in direct contact with the wire strands, so there is no tearing or other damage to the wire. However, the spec sheet does not specify the acceptable wire types, and I can’t seem to find anything with a Google search. It might be worth contacting Buchanan/Ideal to see if they have better info.

Brian Teitelbaum

AEE Solar

*From:*RE-wrenches [mailto:[email protected] <mailto:[email protected]>] *On Behalf Of *Jeremy Rodriguez
*Sent:* Wednesday, August 10, 2016 6:32 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Pass through/transition box for Enphase

How about these?

https://idealind.com/us/en/products/wire-termination/set-screw-connectors/set-screw-connectors/set-screw-wire-connectors.aspx

Jeremy Rodriguez

Solar Installation And Design Expert

All Solar, Inc.

1463 M St

Penrose Colorado 81240

Sent by Jeremy's iPhone. Sorry for typos and shorthand!


On Aug 8, 2016, at 2:00 PM, Benn Kilburn <[email protected] <mailto:[email protected]>> wrote:

    Din rail mounted terminal blocks.... Weidmuler WDU6 or WDU10,
    depending on the wire size you are using.

    Benn Kilburn

    SkyFire Energy Inc.

    780-906-7807


    On Aug 8, 2016, at 12:49 PM, Jason Szumlanski
    <[email protected]
    <mailto:[email protected]>> wrote:

        I'm looking to bring 8 Enphase 240V circuits in multiple
        conduits into an enclosure inside the attic where I can
        transition to Romex. I'd rather use some kind of rail mounted
        terminals in an enclosure or something rather than making
        splices in a generic j-box. I'm not looking to combine
        circuits - just transition from THWN to Romex and keep things
        neat an organized.

        Any sugg

[The entire original message is not included.]



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to