Yes, wire nuts, and loose connections are a big issue in AC circuits as
well. One of my most frequent troubleshooting calls is tracing out
loose/burnt/arcing connections behind receptacles and switches. Usually
caused by sloppy workmanship, or contractors being in a hurry.
Mike

On Tue, Sep 6, 2016 at 12:14 PM, Glenn Burt <[email protected]> wrote:

> Be aware that SMA explicitly prohibits the use of wire nuts in their
> installation instructions on the DC input circuits.
> ------------------------------
> From: Jerry Shafer <[email protected]>
> Sent: ‎9/‎6/‎2016 14:32
> To: [email protected]
> Subject: Re: [RE-wrenches] Wire nuts
>
> Wrenches
> Better pic
>
> On Sep 5, 2016 4:52 PM, "Jerry Shafer" <[email protected]> wrote:
>
>> To my fellow wrenches
>> It comes up every so often and with DC, I will not use, approve or pass
>> any wire nuts on any DC side. Some say its OK but the facts are they will
>> fail, this connection was just six years and when l opened the junction box
>> it was glowing and by the looks of it has for some time. There are 8
>> strings 2 per string and thats a 12.5 % failure rate (the other one was
>> completely distroyed) not to mention the fire hazard in a PVC junction box.
>> Please pass this along and tell everyone to stop using these.
>> Jerry
>>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/[email protected].
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Michael & Jessica Nelson
MD Electric & Solar Inc.
Office: 707-884-1862
Cell: 707-684-0064
*We prefer to have ALL documentation E-mailed ** prevent paper waste***
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to