I was just called last week to a three phase Enphase system installed by others with three of eight strings that were exhibiting erratic voltages on random phases. First I checked the combiner panels and everything checked out. I went to the roof and discovered that wet rated wire nuts were used (red). The first of eight j-boxes that I opened, I just pushed a wire a little and heard crackling sounds. I didn't have to go any further... bad connections. Problem identified.
So the question remains... what ARE you using? There is a recent thread about fine stranded wire and Polaris taps not being acceptable. There are also people using Alumiconn and Polaris black connectors, which are not rated for wet/damp locations. This all ties in together in terms of best practices in roof junction/transition boxes. Jason Szumlanski On Tue, Sep 6, 2016 at 3:19 PM, August Goers <[email protected]> wrote: > Are those wire nuts listed for wet locations? Most ideal outdoor > (damp/wet) rated wire nuts are blue or grey in my experience. > > > > August > > Luminalt > > > > *From:* RE-wrenches [mailto:[email protected]] *On > Behalf Of *Benn Kilburn > *Sent:* Tuesday, September 06, 2016 12:02 PM > *To:* RE-wrenches > *Subject:* Re: [RE-wrenches] Wire nuts > > > > The reason i'm asking is that the only time i have seen a short, > first-hand, in a wire nut, was because it appeared that one wire was pushed > down rather than binding with the other wire, which would have happened if > the wires were not held tightly when the nut was twisted on. Also, it was > a stranded wire (that was pushed down) being connected to a solid wire, > which is acceptable, but care must be taken to do it properly. > > Also, on all the Ideal wire nut packages I have, the instructions say to > twist the wire nut on until there are two visible twists in the wire. I > suppose this is to ensure the twist/connection is sufficient to make a > solid connection and perhaps to keep the wires together if the wire nut is > removed. > > The ones in this photo do not look like they were installed as per the > instructions, which brings how much attention was put in to installing them > in the first place. > > I've always questioned the why wire nuts are cautioned against, especially > considering how many wire nuts are used in residential and commercial > jobs. I'm sure if there was a legit issue with them then insurance > companies would insist they not be used, such as aluminum wiring? > > > *Benn Kilburn * > > CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc > > 14515 – 121A Ave NW | Edmonton, AB | T5L 2T2 > > P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com > > [image: email] <[email protected]> [image: facebook] > <https://www.facebook.com/SkyFireEnergy> [image: twitter] > <https://twitter.com/SkyFireEnergy> [image: linkedin] > <https://www.linkedin.com/company/283735?trk=tyah&trkInfo=tarId%3A1408655033432%2Ctas%3Askyfire%2Cidx%3A2-2-5> > > > [image: SkyFire Energy Logo_horizontal] > > *WE HAVE MOVED!** Please note our new address above.* > > > > On Tue, Sep 6, 2016 at 12:47 PM, Jerry Shafer <[email protected]> > wrote: > > All the other nuts are tight so l cant not say it was or not but l see > this alot and this was one that was caught just at the right time. > Jerry > > > > On Sep 6, 2016 8:44 AM, "Benn Kilburn" <[email protected]> wrote: > > Jerry, > > Can you confirm that this was caused by a failure of the wire nut, itself, > and not due to user error (not properly stripping enough jacket, inserting > even length wires and sufficiently twisting on the wire nut) > > Benn Kilburn > > SkyFire Energy Inc. > > 780-906-7807 > > > On Sep 6, 2016, at 12:32 PM, Jerry Shafer <[email protected]> > wrote: > > Wrenches > Better pic > > > > On Sep 5, 2016 4:52 PM, "Jerry Shafer" <[email protected]> wrote: > > To my fellow wrenches > It comes up every so often and with DC, I will not use, approve or pass > any wire nuts on any DC side. Some say its OK but the facts are they will > fail, this connection was just six years and when l opened the junction box > it was glowing and by the looks of it has for some time. There are 8 > strings 2 per string and thats a 12.5 % failure rate (the other one was > completely distroyed) not to mention the fire hazard in a PVC junction box. > Please pass this along and tell everyone to stop using these. > Jerry > > <2016-09-06 08.29.40.jpg> > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/[email protected]. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/[email protected]. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/[email protected]. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: [email protected] > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/[email protected]. > org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > >
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org