Do you mean beyond the NEC listing violation?

-----Original Message-----
From: "Benn Kilburn" <[email protected]>
Sent: ‎9/‎6/‎2016 19:21
To: "RE-wrenches" <[email protected]>
Subject: Re: [RE-wrenches] Wire nuts

August, et al,
Do you have any issues with crimping the fine wires that are typically on a 
microinverter cable, to a coarse stranded or solid wire? 
Or, do you know if there is an issue with using these crimps with fine stranded 
wire?

Benn Kilburn
SkyFire Energy Inc. 
780-906-7807

> On Sep 6, 2016, at 3:55 PM, August Goers <[email protected]> wrote:
> 
> We’re using ideal/Buchanan splice cap crimp connectors as I’ve posted here a 
> couple of times:
>  
> http://www.idealind.com/ideal-electrical/us/en/products/wire-termination/60-crimp-connectors/copper-splice-cap-crimp-connectors.aspx
>  
> We really like these in nearly every way. I just spoke with Ideal on the 
> phone to verify their listing for damp/wet locations. They gave me a verbal 
> okay to use them in outdoor boxes, but don’t have any documentation providing 
> a specific listing for this purpose. This puts us in a bind, but they still 
> seem like the least of all evils.
>  
> It looks from Jerry’s picture that the box got wet inside. You can see signs 
> of dirty water intrusion towards the back of the box and the wires look they 
> were once muddy as well. The outdoor rated wire nuts that are pre-packed with 
> grease likely would have been okay in a very wet box provided they were 
> assembled properly. We are putting weep holes in our boxes and conduit bodies 
> because we’ve had multiple issues with water flooding boxes and conduits. 
> Dirty conductive water and 600 VDC don’t mix well.
>  
> August
>  
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of Jason Szumlanski
> Sent: Tuesday, September 06, 2016 1:25 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Wire nuts
>  
> I was just called last week to a three phase Enphase system installed by 
> others with three of eight strings that were exhibiting erratic voltages on 
> random phases. First I checked the combiner panels and everything checked 
> out. I went to the roof and discovered that wet rated wire nuts were used 
> (red). The first of eight j-boxes that I opened, I just pushed a wire a 
> little and heard crackling sounds. I didn't have to go any further... bad 
> connections. Problem identified.
>  
> So the question remains... what ARE you using? There is a recent thread about 
> fine stranded wire and Polaris taps not being acceptable. There are also 
> people using Alumiconn and Polaris black connectors, which are not rated for 
> wet/damp locations. This all ties in together in terms of best practices in 
> roof junction/transition boxes.
>  
>  
> ​Jason Szumlanski​
> 
>  
>  
>  
> On Tue, Sep 6, 2016 at 3:19 PM, August Goers <[email protected]> wrote:
> Are those wire nuts listed for wet locations? Most ideal outdoor (damp/wet) 
> rated wire nuts are blue or grey in my experience.
>  
> August
> Luminalt
>  
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of Benn Kilburn
> Sent: Tuesday, September 06, 2016 12:02 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Wire nuts
>  
> The reason i'm asking is that the only time i have seen a short, first-hand, 
> in a wire nut, was because it appeared that one wire was pushed down rather 
> than binding with the other wire, which would have happened if the wires were 
> not held tightly when the nut was twisted on.  Also, it was a stranded wire 
> (that was pushed down) being connected to a solid wire, which is acceptable, 
> but care must be taken to do it properly.
> 
> Also, on all the Ideal wire nut packages I have, the instructions say to 
> twist the wire nut on until there are two visible twists in the wire.  I 
> suppose this is to ensure the twist/connection is sufficient to make a solid 
> connection and perhaps to keep the wires together if the wire nut is removed.
> 
> The ones in this photo do not look like they were installed as per the 
> instructions, which brings how much attention was put in to installing them 
> in the first place.
> 
> I've always questioned the why wire nuts are cautioned against, especially 
> considering how many wire nuts are used in residential and commercial jobs.  
> I'm sure if there was a legit issue with them then insurance companies would 
> insist they not be used, such as aluminum wiring?
> 
> Benn Kilburn 
> CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
> 14515 – 121A Ave NW | Edmonton, AB | T5L 2T2
> P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
>     
> 
> WE HAVE MOVED! Please note our new address above.
>  
> On Tue, Sep 6, 2016 at 12:47 PM, Jerry Shafer <[email protected]> 
> wrote:
> All the other nuts are tight so l cant not say it was or not but l see this 
> alot and this was one that was caught just at the right time. 
> Jerry
> 
>  
> On Sep 6, 2016 8:44 AM, "Benn Kilburn" <[email protected]> wrote:
> Jerry,
> Can you confirm that this was caused by a failure of the wire nut, itself, 
> and not due to user error (not properly stripping enough jacket,  inserting 
> even length wires and sufficiently twisting on the wire nut)
> 
> Benn Kilburn
> SkyFire Energy Inc. 
> 780-906-7807
> 
> On Sep 6, 2016, at 12:32 PM, Jerry Shafer <[email protected]> wrote:
> 
> Wrenches
> Better pic
> 
>  
> On Sep 5, 2016 4:52 PM, "Jerry Shafer" <[email protected]> wrote:
> To my fellow wrenches
> It comes up every so often and with DC, I will not use, approve or pass any 
> wire nuts on any DC side. Some say its OK but the facts are they will fail, 
> this connection was just six years and when l opened the junction box it was 
> glowing and by the looks of it has for some time. There are 8 strings 2 per 
> string and thats a 12.5 % failure rate (the other one was completely 
> distroyed) not to mention the fire hazard in a PVC junction box.
> Please pass this along and tell everyone to stop using these. 
> Jerry
> 
> <2016-09-06 08.29.40.jpg>
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
>  
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 


[The entire original message is not included.]
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to