Hello William,

How about using an Outback Flexware 500/1000 AC circuit breaker box with DC 
rated DIN rail mounted breakers?  The Main breaker might need to live in the 
GSLC though…..

Best,

Jason Lerner

Waldron Power and Light Co.

> On Oct 10, 2016, at 2:55 PM, William Miller <[email protected]> wrote:
> 
> Friends:
>  
> I am looking for a PV recombiner.  I need to accept the outputs from 3 remote 
> PV Combiners, send those outputs through GFP circuit breakers, into charge 
> controllers, back thorough breaker, into a bus bar, through a main breaker 
> and onto a large battery bank.
>  
> I am using 2 Outback Radian inverters, but I refuse to install DC breakers on 
> their dead-front because wiring to studs facing away from the front is an 
> inferior design.  Furthermore, I see no need to run PV circuits through the 
> GSLC cabinets.
>  
> I looked at the Midnite MNDC15 but again, these use panel mounted breakers 
> with studs on the back.
>  
> Anyone know of a more thoughtfully designed PV recombiner?
>  
> Thanks in advance,
>  
> William Miller
>  
>  
> <image003.jpg>
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected] 
> <mailto:[email protected]>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html 
> <http://www.mail-archive.com/[email protected]/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to