WrenchesI think its in the inverter or battery but somewhere before it leaves
the inverter flickering lights indicates the inverter is seeing the issue up
close, a 4 k inverter is 33 amps AC but Over 166 from the 24 volt batteries if
the load if half that with lights and inverter is strugling need to look at the
battery voltage including cable drop. I have seen this quite a few times over
the years.Jerry
Sent from my Verizon, Samsung Galaxy smartphone
-------- Original message --------
From: Darryl Thayer <[email protected]>
Date: 2/9/18 5:25 PM (GMT-10:00)
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] 1/2 HP well pump soft start at 120 VAC
Dana my 1/2 HP 240 volt pump draws about < 2 amps, which is maybe 3.3 amps if
it is 120 volts. I wonder if the high volt drop is leaving your pump in locked
rotor for a long time, in which case a soft start will not help. Perhaps a
buck-boost transformer (about 150 watts) boosting 16% would get the pump
started faster? Do the wire size and length for calculating volt drop. then
use a 3.3 amp soft start.
On Fri, Feb 9, 2018 at 6:24 PM, <[email protected]> wrote:
Hi Dana,
We have been using Grundfos SQ-O 1/2 hp, 5 GPM (or they have a 10 GPM
model) soft start pumps for years, with great outcomes. We have sold 60
or so over the years with no returns.
Daryl
> Hey all you solar wise guys,
>
>
>
> I am looking for a recommendation based on your experience, not just data
> sheets for a 120 volt-9.8 amp-1/2HP well pump soft starter. Every time the
> well pump starts the SW4024 groans and the lights flicker.
>
>
>
> There are a lot of units that claim to soft start a ½ HP, but the reality
> is
> that they claim ½ HP but are limited to 3.3 amp+/- output. I asked how
> this
> is and was met with the usual, “gee gosh I am not sure.” I have one in
> hand
> now from ABB that is guilty of this claim.
>
>
>
> Some units claim to meet the spec but then you must limit the wire length
> to
> 30 meters. The well is 150’ from the house & 120 ft deep so a 270’ wire
> run
> with what the well guy threw in 18 years ago. VFW cable [multi strand
> cable]
> is a partial answer but not down in the well.
>
> Somewhere down the road the inverter & the well pump will get replaced but
> for now it is working. The newer 3PH wild AC drives are amazing on a
> Radian
> Inverter. You cannot even tell the well is pumping till it has been for a
> while and the fans kick on.
>
>
>
> Suggestions & directions that have proven reliable for you?
>
> Thanks.
>
>
>
>
>
> ----------------------------------------------------------------------------
>
> Dana Orzel Great Solar Works, Inc.
>
> C - 208.721.7003 [email protected]
>
> Idaho Contractor - # 028765 Idaho PV # 028374
>
> NABCEP # 051112-136 www.solarwork.biz
> <http://www.solarwork.biz>
>
> "Responsible Technologies for Responsible People since 1988"
>
> P Please consider the environment before printing this email.
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org