That is interesting about Magnum: Tech support
told me that the 4024PAE was two separate 2000 W
inverters. We had problems with a microwave shutting the system down.
Do you find you have good reliability with Magnum products?
Drake
At 03:53 PM 5/30/2018, you wrote:
HI Dave and everyone, Its interesting because
there is a great deal of difference between
OEMâs. Outback says 4kw at 120v for 8kw
radian. ( tech support) Magnum says 27 amps at
120v, 16.7 amps at 240 for MS4024PAE ( from the
manual) Schneider says 4200 watts at 120v on
XW-6848 ( from the manual) Also I know that the
Magnum allows you to charge with just 120v and I
think the XW is the same, OB you have to have
240v. Cheers jay > On May 30, 2018, at 7:52 AM,
Dave Angelini Offgrid Solar
<[email protected]> wrote: > > The 8kw radian
still has to have balance! You can't expect it
to supply > 8kw @ 120vac. It can supply 8kw @
240 vac. > > >> Does each of the 4 kW 240 volt
inverters have a maximum on the 120-volt >>
power it can supply? for example, can it supply
70% of the 4 kW on 120 >> -volts? >> This
example would leave 5.6 kW of 120-volt? >> >> On
Tue, May 29, 2018 at 11:09 PM, jerrysgarage01 >>
<[email protected]> >> wrote: >> >>> The
Radian has 2, 4k, 240 volt inverters, so its
different but the way >>> the >>> computer works
it makes the same from the load side of
things >>> Jerry >>> >>> >>> >>> Sent from my
Verizon, Samsung Galaxy smartphone >>> >>> >>>
-------- Original message -------- >>> From:
frenergy <[email protected]> >>> Date: 5/29/18
5:51 PM (GMT-10:00) >>> To:
[email protected] >>> Subject:
[RE-wrenches] Xfmr's job? >>> >>> Hey
folks, >>> >>> Outback FP2 with Xfrmr
shifts power to "other" leg if that >>> leg
needs more than the one FX can provide,
right? Say, you need 5.5 KW >>> on leg 1, the
Xfrmr pulls some power from the leg 2 (inverter)
to >>> support that 5.5KW load on leg 1. >>> >>>
My question (assuming above is accurate) is does
the 8048 Radian do the >>> same? >>> >>>
Thanks, >>> >>> Bill >>> >>> Feather River Solar
Electric >>> Bill Battagin, Owner >>> 4291
Nelson St. >>> Taylorsville, CA 95983 >>>
530.284.7849 >>> CA Lic 874049 >>>
www.frenergy.net >>> >>> >>> ---
_______________________________________________
List sponsored by Redwood Alliance List Address:
[email protected] Change
listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm Check out or
update participant bios: www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org