I don't think its worth all that rewiring now to preserve an imperfect battery design that's probably only going to last a few more years anyway.  Just use those batteries up, and come in with a new single or double string of larger batteries.

I know all of us wrenches would like to see amp circulation between strings with some scientific accuracy, but is that in the customer's best interest?

Ray Walters
Remote Solar
303 505-8760

On 7/23/18 10:33 AM, [email protected] wrote:

There will be troubleshooting with this design. Probably easier to use it up and redesign. If my name was on the inheritance,

I would do it now or at the minimum fuse the strings.

On Mon, 23 Jul 2018 12:26:32 -0400, Chris Schaefer <[email protected]> wrote:

And it's not a bad idea to add a shunt in each string for trouble shooting down the road.
Christopher

On Mon, Jul 23, 2018 at 11:24 AM, Steve Higgins <[email protected] <mailto:[email protected]>> wrote:

    I would at least rewire them like this...
    image.png
    Remember all the parallel strings take offs must be the same
    size/length, otherwise you are going to exacerbate imbalance issues.

    <http://www.rollsbattery.com>
    Steve Higgins ⋅ Technical Services Manager
    t+1.902.597.4020 m +1.206.790.5840
    f+1.902.597.8447 [email protected] <mailto:[email protected]>
    <http://www.facebook.com/RollsBattery>
    <http://www.twitter.com/RollsBattery>
    <https://www.youtube.com/user/RollsBattery>
    
<https://www.linkedin.com/company/rolls-battery-engineering><http://www.instagram.com/RollsBattery>

    ------------------------------------------------------------------------
    CONFIDENTIALITY: The information transmitted herein is intended
    only for the addressee and may contain confidential, proprietary
    and/or privileged material. Any unauthorized review, distribution
    or other use of or the taking of any action in reliance upon this
    information is prohibited. If you receive this email in error,
    please contact the sender and delete or destroy this message and
    all copies.
    ------------------------------------------------------------------------

    On Mon, Jul 23, 2018 at 7:24 AM Jerry Shafer
    <[email protected] <mailto:[email protected]>> wrote:

        Dave
         Its a good idea to think of batteries the same way you do PV
        Modules. Any time you have more then two strings they get
        individual fuse protection, this is also good for diagnoses
        purpuses too.
        The current installation has no protection, safety and l
        would change it.
        As far as operation goes it works but thats not a exceptable
        reason to leave it that way is.
        Jerry

        On Mon, Jul 23, 2018, 6:56 AM Dave Tedeyan
        <[email protected] <mailto:[email protected]>> wrote:

            Since we are on the topic of bad battery practices...
            I may be fixing up a system that was both designed and
            installed very poorly.
            They have a 24V Outback VFXR inverter, and ten 12V AGM
            batteries wired into
            5 parallel strings. I know that is a bad idea, but since
            they already have the
            equipment, are there any safety issues by re-using this
            equipment? It is for a
            grid tie battery backup system that will remain in float
            most of the time. I assume
            that the batteries will not last particularly long, but
            is there any harm in using them
            and then just getting new batteries once they fail?
            Stringing is shown in the attached picture.
            Cheers,
            Dave

            *--*
            **
            *Dave Tedeyan
            *
            *Senior Engineer*
            *Taitem Engineering, PC*
            10 Verizon Lane, Lansing, NY 14882
            Voice: (607) 930-3481 x6
            www.taitem.com <http://www.taitem.com/>
            _______________________________________________
            List sponsored by Redwood Alliance

            List Address: [email protected]
            <mailto:[email protected]>

            Change listserver email address & settings:
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

            List-Archive:
            
http://www.mail-archive.com/[email protected]/maillist.html

            List rules & etiquette:
            www.re-wrenches.org/etiquette.htm
            <http://www.re-wrenches.org/etiquette.htm>

            Check out or update participant bios:
            www.members.re-wrenches.org
            <http://www.members.re-wrenches.org>

        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        
http://www.mail-archive.com/[email protected]/maillist.html

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>



--

Chris Schaefer's
<http:www.solarandwindfx.com>
/Tel/Fax 585-229-2083 or Cell 585-748-1870
//5115 South Hill Road ~ Canandaigua New York 14424
//www.solarandwindfx.com <http://www.solarandwindfx.com> ~ E-mail: [email protected] <mailto:[email protected]>/

/
/

Thomas Jefferson, the author of our great Constitution, once said, "democracy" will cease to exist when you take away from those who are willing to work and give to those who would not."



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to