Friends:

I have seen utilities misappropriate values from their meter to the billing. 
That might explain your discrepancies. 

William

> On Aug 16, 2018, at 7:57 AM, Lorenzo Ortiz <[email protected]> wrote:
> 
> Fun fact: Sometimes the stickers on the CT's are incorrect too. Had that 
> happen and took forever to figure out... 
> 
>> On Wed, Aug 15, 2018 at 4:10 PM, Kirpal <[email protected]> wrote:
>> Jason...not sure about the Enphase consumption monitoring, if it is done 
>> with CT's confirm that your CT's are facing the right direction.  Some CT's 
>> are directional and perhaps your consumption monitoring could be backwards 
>> instead of the utility meter wiring backwards.....Seems like the utility 
>> would have noticed incorrect wiring in their can.
>> We use the E Gauge CT clamps for some monitoring and they are directional.  
>> I am not familiar with the Enphase versions.
>> 
>> 
>> Sunny Regards,
>> Kirpal Khalsa
>> Oregon LRT#25
>> NABCEP Certified PV Installation Professional
>> Oregon Solarworks LLC
>> www.oregonsolarworks.com
>> 541-299-0402
>> 
>>> On Wed, Aug 15, 2018 at 4:01 PM, Jason Szumlanski 
>>> <[email protected]> wrote:
>>> Is it possible for a utility meter to be programmed/wired backward? I have 
>>> a client on an Enphase system with production and consumption monitoring, 
>>> and the Enphase monitoring is showing solar production exceeded consumption 
>>> by 400 kWh for a billing period. However, the meter is reading almost 
>>> exactly the opposite. It seems too coincidental.
>>> 
>>> I'm going to go out to the site tomorrow to shut down all of the loads and 
>>> see what happens when solar is only backfeeding the meter, but I'm curious 
>>> how the meters are "programmed" or set up to work.
>>> 
>>> Note that the meter was zeroed to start and the initial billing period 
>>> readings show DEL exceeded REC by 400 kWh, which matches what was billed 
>>> (net usage of positive 400 kWh). 
>>> 
>>> Jason Szumlanski
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: [email protected]
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: [email protected]
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> 
> 
> 
> 
> -- 
> Lorenzo Ortiz   Commercial PV Designer
> 
>     [email protected]  (530) 274-3671
>   
> 
> 
> 
> Showroom located at: 149 E Main St. Grass Valley, CA 95945
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to