Hi Allan,

All LFP batteries can be charged to a much higher voltage than we will ever 
use. Some as high as 4.2Vpc. A disconnect voltage of 3.8 Vpc is typical 
protection voltage for LFP batteries which is below the well maximum charge 
voltage. Some recommend charging to 3.65Vpc, others a little less. 56.4 is low 
at 3.52V. Our cell balancers don’t even start to function until 3.5 volts and 
above. Using a  low voltage can also cause a problem with the SoC calculations.

Using a Trimetric is easy if you use a high enough charge voltage of 3.55Vpc or 
higher and charge at .5C or less.  
You can use L1 settings only, P7 Off. 
Simply setup the reset parameter P1 voltage about 0.2V below charge voltage. 
Leave P2 Charge Amps off. 
Set P3 AH to match actual capacity. 
When voltage parameter is met, you are close enough and it resets to 100%. This 
is due to internal resistance. Your voltage will not go high until you are at 
about 98% or so.

FWIW, if your concern is about harming the Li cells, we have never had a single 
cell failure. We have had several ruined cells from neglect caused by over 
discharging when people did not follow EMS assembly instructions. With 4 cells 
in a 12 volt battery pack, I am talking about thousands of cells we have sold 
in the last 5 years. LFP is rugged, very fast to charge and will last a long 
time with little care.

When I read things about Li batteries on the internet, it makes my head spin 
from all the folklore, falsehoods and fear-born myths. Careful what you read.

Larry Crutcher
Starlight Solar Power Systems


On Aug 21, 2018, at 12:26 PM, Sindelar Solar <[email protected]> wrote:

Yes, I just did. Ralph retired last year and I spoke with the new owner. In 
short, little change - use 2% of capacity for amp threshold and set CEF to 98% 
from default 94%. I was also told to stick with the default 14.1V voltage 
threshold, but that equates to 56.4V for a 48V system, which is above the 
normal range of these batteries, so I'm reluctant to take that advice.

I'm working with Kyle Bolger of Blue Planet on this first installation, and 
will post to the list what I learn that will benefit others.

Thank you, Allan


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to