Hi Daniel,
That is good information. Thanks for the link.
My take on non vented heaters is that they are a
bad idea for general use. They do have the virtue
of allowing off gridders to take winter vacations
without worrying about frozen pipes or dead
batteries. Inverters can be switched off and
charge controllers left on, so batteries will
stay charged. They are also a good emergency
source of heat. Windows can be cracked for ventilation if necessary.
Best,
Drake
At 05:56 PM 8/24/2018, you wrote:
Content-Type: multipart/alternative;
boundary="----=_NextPart_000_0087_01D43BD3.BA477350"
Content-Language: en-us
Drake,
The best thing to minimize blower power draw will be two fold.
* Get the smallest BTU furnace you are
allowed to (with and ECM blower). Since blowers
are generally sized at a nominal CFM/BTU of
heat output. (Around 30CFM/ 1000BTU for the
usual heat pump or 90+eff furnaces)
* Minimize head loss in the duct system.
Head loss has an exponential effect on energy
use as a whole (blower motor and fuel efficiency)
* Bigger distribution ducts
* metal duct for corners and turns (i.e use good fittings)
* little to no flex duct unless for straight runs
i. flex duct always well supported and
pulled tight, little to no slack allowed in a flex duct job.
* Etc
Good read in this article, and the
attached presentation download:
<https://www.energyvanguard.com/blog/secret-moving-air-quietly-through-your-duct-system>https://www.energyvanguard.com/blog/secret-moving-air-quietly-through-your-duct-system
Not knowing the home layout and specs it hard to
give specific advise on that side, but those two
items are big drivers on actual power needs for
blowers. But as you said, the furnace is there
for insurance costs, not primary heating
Also, the unvented propane heater in a primary
dwelling seems like a bad idea to me. Is the
home expected to be well sealed for air leaks?
Blower door tested, relatively well sealed would
be a blower door number of less than 2-3 ACH50
(air changes per hour @ a 50pascal pressure
difference to the outdoors), 1-1.5 is really
good, and passive house is 0.6 and lower?
Because both the fireplace and the unvented
heater could be bad news if thats the case
Something you might want to see if you client is
conscious of. (Not sure how far you are getting
involved in the home design Drake.)
With Regards,
Daniel Young,
NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90
From: RE-wrenches
<[email protected]> On Behalf Of Drake
Sent: Friday, August 24, 2018 4:52 PM
To: RE-wrenches <[email protected]>
Subject: Re: [RE-wrenches] Forced air Furnace
A wood stove heats the house, and will be the
primary source of heat. An un-vented propane
wall heater is installed and can heat the small,
earth bermed, well insulated structure. A
furnace will be a nice supplement, and will
quickly pay for itself in insurance savings.
During even a moderately cloudy day, it will be
fine, but will not be used much on batteries.
Still, I'd like as efficient a model as possible.
If I can find a unit with a 400 W draw, like the
one in our on grid house, that would be
adequate. The specifications I've found on the
blower motors are sketchy. I will likely need to
order it on line (or take a trip to a
neighboring city), so reading the nameplates might not be so easy.
Does anyone know how to get accurate data on furnace blower motors?
Thanks,
Drake
At 01:59 PM 8/24/2018, you wrote:
Content-Type: multipart/alternative;
boundary="------------914ACDD867C6488AACA07365"
Content-Language: en-US
I always try to talk the client into hydronic
heating with ECM drive circulation pumps. They
do make ECM drive blower motors that can be
retrofitted in some furnace systems. Overall,
its just a bad combination off grid: the worse
the weather is the less PV production you have,
and this corresponds to the same time that the
furnace is operating 12 hours/ night. They are
either running the generator a bunch, or waking
up in the morning to a cold house with the power
off, and dead batteries. If its an AC coupled
system, they won't even have any PV production
the next morning either. This is another reason
AC coupled is not a great idea, or at least you
need to always have some DC coupled PV as well, but I digress......
Ray Walters
Remote Solar
303 505-8760
On 8/23/18 5:43 PM, Dana wrote:
Drake,
All the conventional units I have amp clamped
over the years are pushing 900-900+ watts per
hour. I do not recommend them ever & to date I
have never found a lower wattage blower. I would
assume that a permanent magnet motor would fit
this suggestion, but I have not found one.
For off grid I recommend: Radiant floor heat
first and hot water base board second long
before hot air. Air is a better insulator than a heat transfer agent.
The new ECM (electronically commutated motors)
pump motors are basically at DC permanent magnet
motor power draws [Taco & Grundfoss] these days.
Best of luck with this one.
----------------------------------------------------------------------------
Dana Orzel Great Solar Works, Inc.
C -
208.721.7003
<mailto:[email protected]>[email protected]
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP #
051112-136 <http://www.solarwork.biz>www.solarwork.biz
"Responsible Technologies for Responsible People since 1988"
P Please consider the environment before printing this email.
From: RE-wrenches
<mailto:[email protected]><[email protected]>
On Behalf Of Drake
Sent: Thursday, August 23, 2018 2:37 PM
To: RE-wrenches
<mailto:[email protected]><[email protected]>
Subject: [RE-wrenches] Forced air Furnace
Hello Wrenches,
What is the best choice for a propane, forced
air furnace for an off grid house? We would
prefer one that doesn't have a phantom load,
although the transformer for the thermostat may
not be avoidable. Low blower current would be
preferable. The furnace AC will be powered by a Magnum 4448 PAE.
Thank you,
Drake
Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV
740-448-7328
<http://athens-electric.com/>http://athens-electric.com/
_______________________________________________
List sponsored by Redwood Alliance
List Address:
<mailto:[email protected]>[email protected]
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address:
<mailto:[email protected]>[email protected]
Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
<http://www.mail-archive.com/[email protected]/maillist.html>http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
<http://www.members.re-wrenches.org/>www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org