Lorenzo You might want to look at relocating the inverter(s) closer to the meter instead of the array, one reason is even if there is some line loss at full power its less as the voltage goes up and the inverter does not see the line resistance that can cause high voltage issues at the inverter. Some engineers use more side of peak performance than full power, this keeps wite size down and does not effect output Jerry
On Sep 17, 2018 9:42 AM, "Lorenzo Ortiz" <[email protected]> wrote: Wrenches, We have a PV array situated about 900' from the POI (240V 1PH). We initially spec'd (5) 11.4kW inverters and the combined output would be 238A. The wire size required for this current over that distance is cost prohibitive. A solution was to use a single 50kW 3 phase inverter at the array and then convert it to 240V... somehow? Is anyone familiar with how to go about doing this? My thought was to have a step down transformer at the POI and pull off two legs to get 240V. Is this even a thing? The other, more expensive option is to use a step up transformer at the array and a step down at the POI to get us a smaller wire size. Thanks for any input. -- *Loren Ortiz Commercial PV Designer* [email protected] <[email protected]>* (530) 274-3671* <http://californiasolarco.com/referral-program/> *Showroom located at: 149 E Main St. Grass Valley, CA 95945* _______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org