The Fronius Primo line is a single phase product that is rated for 1000VDC. 
-Wes Kennedy  

    On Tuesday, September 18, 2018, 7:28:24 PM MDT, Jay <[email protected]> 
wrote:  
 
 Does anyone make a 1000vdc single phase inverter?Would reduce wire costs 
dramatically 
JayPeltz power. 
On Sep 18, 2018, at 11:36 AM, Lorenzo Ortiz <[email protected]> wrote:


Thanks for all the input guys.  After looking at the 3 phase with transformer 
options with some transformer manufacturers, that has been pretty much ruled 
out due to complexity/cost. With single phase step-up and step-down 
transformers, even at 600VAC, it still requires some monster wire.The best 
solution seems to be placing the inverters next to the POI and just running 
long strings from the array back to the inverters and accepting up to 4%-5% 
voltage drop. And that's with #8 instead of the usual #10 AND accounting for 
worst-case production.
Man, sometimes this solar stuff is just crazy...
On Tue, Sep 18, 2018 at 10:15 AM, Blake Gleason <[email protected]> 
wrote:

Good advice already on this thread.  A couple of points to consider:
1. Re: step-up/step-down option (probably what I'd do): definitely pay 
attention to transformer spec to minimize both magnetization and operating 
losses.  Newer DOE 2016-compliant transformers are MUCH better than before, and 
that's just the minimum standard.  If you really want to minimize magnetization 
losses, you can always design a relay/timer to disconnect the transformers at 
night (from the interconnection side), although I've found that this setup is 
either very expensive or too unreliable (nuisance tripping upon re-connect, 
timer gets "off" cycle somehow, etc).
2. I think someone mentioned a 480V single-phase inverter.  I'm not aware of a 
high-quality product meeting that description.  Is there one?  All of the 
"480V" single-phase inverters I'm aware of are 277V (line to neutral), which is 
hardly worth the transformer effort (versus 240V).
3. Definitely use aluminum wire for the long run.  If wire size is still too 
large, even with step up/down tranformers, consider allowing slightly increased 
voltage drop at full power (say, 5%), and, depending on typical grid voltage at 
the site, change taps on one of the transformers to err on the low side (from 
inverters' point-of-view), to keep the inverters from tripping at upper voltage 
limit at full power (max voltage drop/rise).

Blake
On Tue, Sep 18, 2018 at 9:57 AM, Jerry Shafer <[email protected]> wrote:

LorenzoYou might want to look at relocating the inverter(s) closer to the meter 
instead of the array, one reason is even if there is some line loss at full 
power its less as the voltage goes up and the inverter does not see the line 
resistance that can cause high voltage issues at the inverter. Some engineers 
use more side of peak performance than full power, this keeps wite size down 
and does not effect outputJerry
On Sep 17, 2018 9:42 AM, "Lorenzo Ortiz" <[email protected]> wrote:

Wrenches,
We have a PV array situated about 900' from the POI (240V 1PH). We initially 
spec'd (5) 11.4kW inverters and the combined output would be 238A. The wire 
size required for this current over that distance is cost prohibitive.
A solution was to use a single 50kW 3 phase inverter at the array and then 
convert it to 240V... somehow? Is anyone familiar with how to go about doing 
this? My thought was to have a step down transformer at the POI and pull off 
two legs to get 240V. Is this even a thing?
The other, more expensive option is to use a step up transformer at the array 
and a step down at the POI to get us a smaller wire size.
Thanks for any input.

-- 
Loren Ortiz   Commercial PV Designer
    [email protected]  (530) 274-3671  


Showroom located at: 149 E Main St. Grass Valley, CA 
95945______________________________ _________________
List sponsored by Redwood Alliance

List Address: [email protected]. org

Change listserver email address & settings:
http://lists.re-wrenches.org/o ptions.cgi/re-wrenches-re-wren ches.org

List-Archive: http://www.mail-archive.com/re [email protected] 
g/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette. htm

Check out or update participant bios:
www.members.re-wrenches.org




______________________________ _________________
List sponsored by Redwood Alliance

List Address: [email protected]. org

Change listserver email address & settings:
http://lists.re-wrenches.org/o ptions.cgi/re-wrenches-re-wren ches.org

List-Archive: http://www.mail-archive.com/re [email protected] 
g/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette. htm

Check out or update participant bios:
www.members.re-wrenches.org






-- 





|  
| 
  |
|  | 
    | 
    | 
   | 
    | 
    | 
    | 
    |

 |  
|  Blake Gleason - PE, LEED AP
Director of Innovation & Technical Excellence |
| 
 P:  510.845.2997 x128 
 E: [email protected] 
W: sunlightandpower.com
  |
| 
See how universities are using business as a force for good with solar! |

  |

 
|  |


______________________________ _________________
List sponsored by Redwood Alliance

List Address: [email protected]. org

Change listserver email address & settings:
http://lists.re-wrenches.org/ options.cgi/re-wrenches-re- wrenches.org

List-Archive: http://www.mail-archive.com/ [email protected]. 
org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette. htm

Check out or update participant bios:
www.members.re-wrenches.org






-- 
Loren Ortiz   Commercial PV Designer
    [email protected]  (530) 274-3671  


Showroom located at: 149 E Main St. Grass Valley, CA 95945

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

  
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to