Here at the Oasis home/office, we have a Goulds 3 hp
240VAC soft start pump (#18GS30, w/ Franklin motor HS09970
and #3AS30 Aquavar Solo controller); it's been running off
of my 2011 Radian GS8048 since 2016, when I had to drill a
new well (the water table is dropping) and pump from about
300 ft. depth.I have 3500 ft. of drip irrigation, a big
garden and the usual domestic water loads.It's worked
flawlessly since its inception, and I cannot speak more
highly of Goulds pumps.My first one lasted 23 years (it
was a 1.5HP model).
Best,
Chris Daum
Oasis Montana Inc.
406-777-4309 or 4321
406-777-4309 fax
www.oasismontana.com <http://www.oasismontana.com>
*From:*RE-wrenches
<[email protected]>
<mailto:[email protected]> *On
Behalf Of *Dana
*Sent:* Friday, July 26, 2019 9:34 AM
*To:* 'Jeff Clearwater' <[email protected]>
<mailto:[email protected]>; 'RE-wrenches'
<[email protected]>
<mailto:[email protected]>
*Subject:* Re: [RE-wrenches] Soft Start Modules for Well
and Sewage Pumps?
Yes I have used soft starts offgrid with SW & VFX for 15+
years, in spite of doing load evaluations & others
installing what ever they normally used. It has been a
great rescue device. Well pump, 2 dish washers, booster
pump, etc.
Dana Orzel Great Solar Works,
Inc.
*C - 208.721.7003 [email protected]
<mailto:[email protected]>*
Idaho Contractor - # 028765 Idaho PV # 028374
NABCEP # 051112-136 www.solarwork.com
<http://www.solarwork.com>
"Responsible Technologies for Responsible People since 1988"
*P*Please consider the environment before printing this email.
*From:*RE-wrenches
<[email protected]
<mailto:[email protected]>> *On
Behalf Of *Jeff Clearwater
*Sent:* Friday, July 26, 2019 8:04 AM
*To:* RE-wrenches <[email protected]
<mailto:[email protected]>>
*Subject:* [RE-wrenches] Soft Start Modules for Well and
Sewage Pumps?
Hey Wrenches,
Anyone have success using soft-start modules on well and
sewage pumps to lower the surge for off-grid inverters?
The baby we are trying to tame is a 2 HP 15 amp, 53 LRA
Omnivore Grinder Pump - LSG200 series - single phase 230 Vac.
Thanks!
Jeff
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin
<https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
Jeff Clearwater wrote on 7/26/19 6:32 AM:
*Thanks Ray and Jerry,
Great to hear from you both with your years of
combined experience :)*
*So yes looking at the 5 sec has me switching back to
a trusty Radian - even then from what you are saying
it may not work.*
And you are right Ray - Outback is careful to rate
the "overload capability" in KVA rather than KW due
most likely to voltage sag of course.
*So this 53 LRA 2 HP motor - if I can only trust the 5
second (50 A) might not start - especially with other
loads on the system?*
*RADIAN SURGE RATINGS:*
*Maximum Output Current*
1 ms peak 100 Amps AC at 240 VAC, 200 Amps AC at 120 VAC
100 ms RMS 70.7 Amps AC at 240 VAC
*Overload Capability*
100 ms surge 16.97 kVa
5 seconds 12 kVa
30 minute 9 kVa
*Other's experience with 2 HP sewage pump or well pump
motors on a Radian?
Thanks!
Jeff*
Ray wrote on 7/25/19 5:48 PM:
I only look at the 5 sec and 30 sec surge ratings
to get an idea what an inverter can really do in
the real world. All those millisecond ratings/ in
rush current specs won't get a pump or motor
started, and will basically just get you into
trouble. The reason they have those ratings in
amps and not watts, is that the voltage craters
during that 100mS surge.
I can't tell you how many times we tried to start
a pump, compressor, or large table saw, and the
inverter just shut off, even though the "in rush
current" was within the theoretical inverter
capacity. Actual Wrench list testimonials are
much more valuable than those arcane specs.
Ray WaltersRemote Solar303 505-8760
On 7/25/19 5:15 PM, Jeff Clearwater wrote:
*Hey There Wrenches,*
So be advised that after a little research the
SW dual stack will NOT double the surge
ratings of a single SW.
But that brings me to my second question:
*
What inverter surge rating should one refer to
when looking at maximum Inrush or LRA - 1ms?
100ms? 1 sec?*
*Your engineering wisdom welcomed!*
Thanks,
Jeff
Jeff Clearwater wrote on 7/23/19 8:27 PM:
Thanks for the tip! I'll check the firmware.
Dave Angelini Offgrid Solar wrote on
7/22/19 9:11 AM:
Hi Jeff,
I am not going to guess if this will
work, it should. I use XW's because
they start anything I have come across.
If you do this, make sure but SW's
have the latest and same firmware.
There were problems with stacked SW's
early on in their development.
**Dave Angelini Offgrid Solar**
**"we go where powerlines don't"**
**http://members.sti.net/offgridsolar/**
**e-mail [email protected]
<mailto:[email protected]>**
**text 209 813 0060**
On Mon, 22 Jul 2019 07:26:07 -0700,
Jeff Clearwater
<[email protected]>
<mailto:[email protected]>
wrote:
Hey Esteemed Wrenches,
So I recently built a power
trailer with a single 4 KW (4048)
Schneider SW for a client with a
moderate cabin lifestyle.
But he lives on a high hill and
even though his 2 HP Macerator is
only rated at 15 amps continuous
that baby starts up with a
whopping kick - probably close to
or at it's 53 Amps Locked Rotor
rating.
*The SW has the following surge
capability:*
*SW 4048 Rated @ 240 Volts:*
Continuous - 15.2 Amps 3700 Watts
30 Minutes - 18.3 Amps 4400 Watts
5 Secs - 29.2 Amps 7000 Watts
Max (100ms?) - 41 Amps - 9840 Watts
Can I be confidant that 2 stacked
SWs will start this baby?
*Any experience with similar
macerators - or simply educated
guesses?
*
Thanks!
Jeff
--
**Dave Angelini Offgrid Solar**
**"we go where powerlines don't"**
**http://members.sti.net/offgridsolar/**
**e-mail [email protected]
<mailto:[email protected]>**
**text 209 813 0060**
_______________________________________________List
sponsored by Redwood AllianceList Address:
[email protected]
<mailto:[email protected]>Change
listserver email address &
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:
http://www.mail-archive.com/[email protected]/maillist.htmlList
rules &
etiquette:www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>Check
out or update participant
bios:www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
_______________________________________________List
sponsored by Redwood AllianceList Address:
[email protected]
<mailto:[email protected]>Change
listserver email address &
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:
http://www.mail-archive.com/[email protected]/maillist.htmlList
rules &
etiquette:www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>Check
out or update participant
bios:www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
_______________________________________________List
sponsored by Redwood AllianceList Address:
[email protected]
<mailto:[email protected]>Change
listserver email address &
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:
http://www.mail-archive.com/[email protected]/maillist.htmlList
rules &
etiquette:www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>Check
out or update participant
bios:www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
_______________________________________________List
sponsored by Redwood AllianceList Address:
[email protected]
<mailto:[email protected]>Change
listserver email address &
settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.orgList-Archive:
http://www.mail-archive.com/[email protected]/maillist.htmlList
rules & etiquette:www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>Check out or
update participant bios:www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin
<https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
<http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org
<http://www.members.re-wrenches.org>