Hi Aaron, 

I think you have to have higher settings and not let the
battery get this low for your triggers. I do not know the capacity but you
are on the edge. When you looked at events, did you look in each device and
under faults and warning in the system section? Two places right? Really
need more data like what are the loads. I really doubt this is altitude or
temp related. 
Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail offgridso...@sti.net
[2]
text 209 813 0060

On Tue, 19 Nov 2019 07:06:15 -0700, Aaron Mandelkorn
wrote:  Thanks all for the info. I did check the auto gen start settings
and and they are set pretty high and at the 15 min, 30 min, and two hr
triggers all above the LCBO setting of 23v. I have hard time believing that
the system is crashing at night due to low battery and doing so so quickly
that the gen isn't coming on. Could this be an issue of temporary voltage
drop triggering the LCBO due to a large load coming on at night? Why would
these events not be in the log and why isn't the generator coming on? A
seems to work during the day and when I come out there to test.

 Aaron
Mandelkorn
President / Founder
Renewable Energy Outfitters
www.reosolar.com
[3]
Off Grid Depot
www.offgridnow.com [4]
970-596-3744   -- 




Links:
------
[1] http://members.sti.net/offgridsolar/
[2]
mailto:offgridso...@sti.net
[3] http://www.reosolar.com
[4]
http://www.offgridnow.com
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to