Thanks all for the info. I did check the auto gen start settings and and they are set pretty high and at the 15 min, 30 min, and two hr triggers all above the LCBO setting of 23v. I have hard time believing that the system is crashing at night due to low battery and doing so so quickly that the gen isn't coming on. Could this be an issue of temporary voltage drop triggering the LCBO due to a large load coming on at night? Why would these events not be in the log and why isn't the generator coming on? A seems to work during the day and when I come out there to test.
Aaron Mandelkorn President / Founder Renewable Energy Outfitters www.reosolar.com Off Grid Depot www.offgridnow.com 970-596-3744
_______________________________________________ List sponsored by Redwood Alliance List Address: [email protected] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/[email protected]/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org