Mike,

 

Thanks for posting the note, but I find the wording to be less than fully
clear. According to this note, the "The transformer-less series of inverters
named Sunny Boy TL-US-12, Sunny Boy TL-US-22 and Sunny Tripower
12/15/20/24000TL-US-10 have a neutral connection that is required at
installation for instrumentation, voltage and phase detection only."

 

There is no mention of the -41 inverter also using the neutral for reference
only, even though the note is "applicable to the following inverter types"
and that shows the -41

Also, the table has these green x marks but no annotation of what the green
x indicates.

Can you clarify, please?

 

 



 

 

 

From: RE-wrenches <[email protected]> On Behalf Of
Harry Mahon
Sent: Thursday, November 14, 2019 11:02 AM
To: RE-wrenches <[email protected]>; Jeff Clearwater
<[email protected]>
Subject: Re: [RE-wrenches] 705.95(B) and Sunny Boys - current on Neutral?

 

Lloyd - great find!

 

I am attaching a updated note that specifically calls out current products
but has less code detail.

 

Best regards - 

Mike

 

SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300

Rocklin, CA 95765

U.S.A.
Mobile:   +1 916 918 9412
www.SMA-America.com <http://www.sma-america.com/> 

 

Solar Academy: https://solaracademy.sma.de/en.html

 

SMA America Solar Academy webinars: 

https://solaracademy.sma.de/en/courses.html

Choose "English" and "Online" as filters.

 

 

 <http://www.facebook.com/pages/SMA-America/140290312717395>
<http://twitter.com/SMA_America>   <http://www.smainverted.com/>
<http://www.linkedin.com/company/364675>
<http://www.youtube.com/playlist?list=PL840A5336CAC32332>
<http://smaadvance.com/signup/>  

 
<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.sma-a
merica.com%2Fhome-systems%2Fpv-solar-and-storage-solutions.html&data=02%7C01
%7CMichael.Mahon%40sma-america.com%7Cc4bcd59d55584c70681208d71b72e485%7Ca059
b96c28294d1188374cc1ff84735d%7C0%7C0%7C637008052588484449&sdata=itzAGcXAYe0x
d5Zhzjuljm6dijJW%2FRGtItHrvxRkrTI%3D&reserved=0> 

 

 

This email and any attachments thereto may contain SMA America, LLC
confidential, privileged and private material for the sole use of the
intended recipient. Any review, copying, or distribution of this email (or
any attachments thereto) by others is strictly prohibited. If you are not
the intended recipient, please contact the sender immediately and
permanently delete the original and any copies of this email and any
attachments thereto. Thank you.

 

From: RE-wrenches <[email protected]
<mailto:[email protected]> > On Behalf Of Lloyd
Hoffstatter
Sent: Wednesday, November 13, 2019 10:38 AM
To: Jeff Clearwater <[email protected]
<mailto:[email protected]> >; RE-wrenches
<[email protected]
<mailto:[email protected]> >
Subject: Re: [RE-wrenches] 705.95(B) and Sunny Boys - current on Neutral?

 

Jeff,

 

An oldie but attached tech note explains.

May Need to upsize G / N  for voltage drop depending on run.

 

Best regards,

 

Lloyd

 

Lloyd Hoffstatter

Sunstruck Consulting

 

Sent from Mail
<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fgo.micros
oft.com%2Ffwlink%2F%3FLinkId%3D550986&data=02%7C01%7Cmichael.mahon%40sma-ame
rica.com%7Ca57263d3340c445bd5ce08d76860354c%7Ca059b96c28294d1188374cc1ff8473
5d%7C0%7C0%7C637092634734737930&sdata=ljnPZYRGhPwgRSsi3yM%2BI46x1iUvt52uQ8Dt
Hvidzvw%3D&reserved=0>  for Windows 10

 

  _____  

From: RE-wrenches <[email protected]
<mailto:[email protected]> > on behalf of Jeff
Clearwater <[email protected]
<mailto:[email protected]> >
Sent: Wednesday, November 13, 2019 12:00:37 PM
To: RE-wrenches <[email protected]
<mailto:[email protected]> >
Subject: [RE-wrenches] 705.95(B) and Sunny Boys - current on Neutral? 

 

Hey Folks,

So does anyone have a reference I can show my AJH as to whether there is any
current on the neutral of a single phase 240 VAC SB 7.7-40 inverter?

705.95(B) states:

Neutral Conductor for Instrumentation, Voltage
Detection or Phase Detection. A conductor used solely for
instrumentation, voltage detection, or phase detection and
connected to a single-phase or 3-phase utility-interactive
inverter, shall be permitted to be sized at less than the
ampacity of the other current-carrying conductors and shall
be sized equal to or larger than the equipment grounding
conductor.

Be great not have to run 3/0 wire to my dedicated PV subpanel with 5 SB7.7s.
At 200 Amps I could use 6 AWG according to 705.95.  A huge savings in wire
pull hassle not to mention copper.

Are there any other practical considerations for those SBs to operate well
if I were to go that low with the neutral?

Anybody have any field experience with AJHs on this?

Thanks,

Jeff

~~~~~~~~~~~

Jeff Clearwater
Village Power Design
linkedin
<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linke
din.com%2Fin%2Fjeff-clearwater-0622a312%2F&data=02%7C01%7Cmichael.mahon%40sm
a-america.com%7Ca57263d3340c445bd5ce08d76860354c%7Ca059b96c28294d1188374cc1f
f84735d%7C0%7C0%7C637092634734747920&sdata=p3O8JIapfJi4lWUaxtjir6oD0Nfss%2Fv
zCc%2BmO6DhkIc%3D&reserved=0>  
www.villagepowerdesign.com
<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.villag
epowerdesign.com&data=02%7C01%7Cmichael.mahon%40sma-america.com%7Ca57263d334
0c445bd5ce08d76860354c%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C63709263
4734747920&sdata=nAk%2FP4sQtocN2rmE64IfGo5BkOo1gemXIBVpP1nWXII%3D&reserved=0
> 
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to