Hi Scot and Mike,

Yes It is terribly worded - an AHJ could easily read it and come away with the impression that only the TL and TriPower required the neutral only for instrumentation and voltage and phase detection - implying the rest used the neutral for current.

And your right what do the x's even mean?

I see the SMA author to be Chris Schwegler authored on July 19th, 2019. Mike, can you send back to him for a re-write as this won't hold it's water to AHJs going forward.

Thanks!

Jeff


[email protected] wrote on 11/26/19 6:42 AM:

Mike,

Thanks for posting the note, but I find the wording to be less than fully clear. According to this note, the “The transformer-less series of inverters named Sunny Boy TL-US-12, Sunny Boy TL-US-22 and Sunny Tripower 12/15/20/24000TL-US-10 have a neutral connection that is required at installation for instrumentation, voltage and phase detection only.”

There is no mention of the -41 inverter also using the neutral for reference only, even though the note is “applicable to the following inverter types” and that shows the -41

Also, the table has these green x marks but no annotation of what the green x indicates.

Can you clarify, please?

simple signature block

*From:* RE-wrenches <[email protected]> *On Behalf Of *Harry Mahon
*Sent:* Thursday, November 14, 2019 11:02 AM
*To:* RE-wrenches <[email protected]>; Jeff Clearwater <[email protected]> *Subject:* Re: [RE-wrenches] 705.95(B) and Sunny Boys - current on Neutral?

Lloyd – great find!

I am attaching a updated note that specifically calls out current products but has less code detail.

Best regards –

Mike

SMA America
Michael Mahon
Technical Trainer, Solar Academy
6020 West Oaks Boulevard, Suite 300

Rocklin, CA 95765

U.S.A.
Mobile: +1 916 918 9412_
www.SMA-America.com <http://www.sma-america.com/>_

__

Solar Academy: https://solaracademy.sma.de/en.html

SMA America Solar Academy webinars:

https://solaracademy.sma.de/en/courses.html

Choose "English" and "Online" as filters.

http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/facebook.jpg <http://www.facebook.com/pages/SMA-America/140290312717395>http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/twitter.jpg <http://twitter.com/SMA_America> http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/wordpress.jpg <http://www.smainverted.com/> Linkedin Logo <http://www.linkedin.com/company/364675> http://sma-planet.sma.de/fileadmin/fm-dam/infos/social_media/youtube.jpg <http://www.youtube.com/playlist?list=PL840A5336CAC32332> SMAAFORUM_ICON <http://smaadvance.com/signup/>

cid:[email protected] <https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.sma-america.com%2Fhome-systems%2Fpv-solar-and-storage-solutions.html&data=02%7C01%7CMichael.Mahon%40sma-america.com%7Cc4bcd59d55584c70681208d71b72e485%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637008052588484449&sdata=itzAGcXAYe0xd5Zhzjuljm6dijJW%2FRGtItHrvxRkrTI%3D&reserved=0>

This email and any attachments thereto may contain SMA America, LLC confidential, privileged and private material for the sole use of the intended recipient. Any review, copying, or distribution of this email (or any attachments thereto) by others is strictly prohibited. If you are not the intended recipient, please contact the sender immediately and permanently delete the original and any copies of this email and any attachments thereto. Thank you.

*From:* RE-wrenches <[email protected] <mailto:[email protected]>> *On Behalf Of *Lloyd Hoffstatter
*Sent:* Wednesday, November 13, 2019 10:38 AM
*To:* Jeff Clearwater <[email protected] <mailto:[email protected]>>; RE-wrenches <[email protected] <mailto:[email protected]>> *Subject:* Re: [RE-wrenches] 705.95(B) and Sunny Boys - current on Neutral?

Jeff,

An oldie but attached tech note explains.

May Need to upsize G / N  for voltage drop depending on run…

Best regards,

Lloyd

Lloyd Hoffstatter

Sunstruck Consulting

Sent from Mail <https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fgo.microsoft.com%2Ffwlink%2F%3FLinkId%3D550986&data=02%7C01%7Cmichael.mahon%40sma-america.com%7Ca57263d3340c445bd5ce08d76860354c%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637092634734737930&sdata=ljnPZYRGhPwgRSsi3yM%2BI46x1iUvt52uQ8DtHvidzvw%3D&reserved=0> for Windows 10

------------------------------------------------------------------------

*From:*RE-wrenches <[email protected] <mailto:[email protected]>> on behalf of Jeff Clearwater <[email protected] <mailto:[email protected]>>
*Sent:* Wednesday, November 13, 2019 12:00:37 PM
*To:* RE-wrenches <[email protected] <mailto:[email protected]>>
*Subject:* [RE-wrenches] 705.95(B) and Sunny Boys - current on Neutral?

Hey Folks,

So does anyone have a reference I can show my AJH as to whether there is any current on the neutral of a single phase 240 VAC SB 7.7-40 inverter?

705.95(B) states:

*Neutral Conductor for Instrumentation, Voltage
Detection or Phase Detection. *A conductor used solely for
instrumentation, voltage detection, or phase detection and
connected to a single-phase or 3-phase utility-interactive
inverter, shall be permitted to be sized at less than the
ampacity of the other current-carrying conductors and shall
be sized equal to or larger than the equipment grounding
conductor.

Be great not have to run 3/0 wire to my dedicated PV subpanel with 5 SB7.7s.  At 200 Amps I could use 6 AWG according to 705.95.  A huge savings in wire pull hassle not to mention copper.

Are there any other practical considerations for those SBs to operate well if I were to go that low with the neutral?

Anybody have any field experience with AJHs on this?

Thanks,

Jeff

~~~~~~~~~~~

Jeff Clearwater
Village Power Design
linkedin <https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Fjeff-clearwater-0622a312%2F&data=02%7C01%7Cmichael.mahon%40sma-america.com%7Ca57263d3340c445bd5ce08d76860354c%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637092634734747920&sdata=p3O8JIapfJi4lWUaxtjir6oD0Nfss%2FvzCc%2BmO6DhkIc%3D&reserved=0> www.villagepowerdesign.com <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.villagepowerdesign.com&data=02%7C01%7Cmichael.mahon%40sma-america.com%7Ca57263d3340c445bd5ce08d76860354c%7Ca059b96c28294d1188374cc1ff84735d%7C0%7C0%7C637092634734747920&sdata=nAk%2FP4sQtocN2rmE64IfGo5BkOo1gemXIBVpP1nWXII%3D&reserved=0>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~



_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to