Hey Folks,

So does anyone have a reference I can show my AJH as to whether there is any current on the neutral of a single phase 240 VAC SB 7.7-40 inverter?

705.95(B) states:

Neutral Conductor for Instrumentation, Voltage
Detection or Phase Detection. A conductor used solely for
instrumentation, voltage detection, or phase detection and
connected to a single-phase or 3-phase utility-interactive
inverter, shall be permitted to be sized at less than the
ampacity of the other current-carrying conductors and shall
be sized equal to or larger than the equipment grounding
conductor.

Be great not have to run 3/0 wire to my dedicated PV subpanel with 5 SB7.7s.  At 200 Amps I could use 6 AWG according to 705.95.  A huge savings in wire pull hassle not to mention copper.

Are there any other practical considerations for those SBs to operate well if I were to go that low with the neutral?

Anybody have any field experience with AJHs on this?

Thanks,

Jeff

~~~~~~~~~~~