Hey Folks,
So does anyone have a reference I can show my AJH as to whether there is
any current on the neutral of a single phase 240 VAC SB 7.7-40 inverter?
705.95(B) states:
Neutral Conductor for Instrumentation, Voltage
Detection or Phase Detection. A conductor used solely for
instrumentation, voltage detection, or phase detection and
connected to a single-phase or 3-phase utility-interactive
inverter, shall be permitted to be sized at less than the
ampacity of the other current-carrying conductors and shall
be sized equal to or larger than the equipment grounding
conductor.
Be great not have to run 3/0 wire to my dedicated PV subpanel with 5
SB7.7s. At 200 Amps I could use 6 AWG according to 705.95. A huge
savings in wire pull hassle not to mention copper.
Are there any other practical considerations for those SBs to operate
well if I were to go that low with the neutral?
Anybody have any field experience with AJHs on this?
Thanks,
Jeff
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~