I just remembered this... There was a tripping breaker here almost
immediately after installation. We investigated the string and found no
issues, including checking the termination cap (on all strings). We reset
the breaker a few times and it would run for days without issue, then trip.
Then we went back once to reset the breaker and heard a huge pop and smoke
was billowing out of a microinverter. It was replaced under warranty. The
system ran for months without issue after that.

Now I'm suspecting that that incident compromised the breaker and it has
been arcing for a while and just manifested itself much later down the line.

The last thing I want to do is have this subpanel and breakers changed out
and then have the incident reoccur. We will double check for water, loose
connections, termination caps, etc, but if there is an internal fault in
cabling or a microinverter, it's kinda hard to nail down these issues
without replacing a whole lot of components.

Jason



On Tue, Jan 21, 2020 at 12:40 PM August Goers <[email protected]> wrote:

> Hi Jason -
>
> It certainly appears that there was some sort of surge or short. We've had
> a few cases where microinverter branch circuit end termination caps were
> left off or fell off and shorted out during rain storms. You might want to
> double check that those are all in place. We've also had cases were
> microinvers themselves developed internal shorts. This third comment is
> only anecdotal - I've been in touch with a couple of other installers that
> have had back-fed breaker issues specifically with Eaton brand breakers
> burning up the bus stabs. Our company has had one unexplained issue where
> the inverter output breaker bus stabs were burned up with Eaton breakers. I
> have no idea whether the breakers were faulty or what, but thought I'd just
> mention it in case there is a pattern.
>
> Best, August
> Luminalt
>
>
> On Tue, Jan 21, 2020 at 9:10 AM Jason Szumlanski <
> [email protected]> wrote:
>
>> (System installed by another contractor...)
>>
>> I have been tasked with assisting in the investigation of damage in a
>> subpanel used to combine inverter output circuits (5 strings of
>> microinverters). There appears to be no damage to conductors or other
>> system components. It looks like the damage started at the stabs of the bus
>> bar where the breakers connect. Picture attached. Here are a few clues:
>>
>>    - Monitoring indicates that damage occurred overnight a few weeks
>>    ago. That night we had rain as a winter front came through Florida,
>>    possibly lightning. The prior day everything was fine.
>>    - The next morning, only 2 of 5 strings started producing power, but
>>    4 of 5 strings were reporting data to the Envoy. The two strings that were
>>    reporting but not producing power reported 0Vac and Voc on the DC side of
>>    the microinverters.
>>    - A couple of weeks later, 1 of the 2 strings that was producing
>>    power quit doing so, but continued reporting data.
>>    - Customer discovered damage yesterday.
>>    - About a week before the initial damage apparently manifested
>>    itself, another contractor installed a whole house generator transfer
>>    switch on the line side of the PV interconnection. The generator has never
>>    been run (there is not even a LP fuel source on site yet). I pointed out
>>    that the solar interconnection, which was previously on the supply side,
>>    would need to be moved to the supply side of the generator transfer
>>    switch's main breaker before operation. During the transfer switch
>>    installation, the contractor also switched line 1 and line 2, but that
>>    shouldn't really matter, except for Enphase consumption monitoring, which
>>    was messed up by the swapping of the lines.
>>
>> So I'm looking for ideas. I'm wondering if the OCPD would be a likely
>> place for lightning damage to manifest itself. I can't visually detect any
>> other damage anywhere else. I can't imagine that the transfer switch
>> installation would have anything to do with it, but the timing is
>> interesting. Other than replacing the subpanel and OCPD and firing it back
>> up (no pun intended), I'm not sure how to approach further investigation.
>>
>> Jason Szumlanski
>> Florida Solar Design Group
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to