Almost every meltdown I've looked at was not due to lightning, but heat from a high resistance connection.  A lug not torqued can cause surrounding plastic to melt.  If the wrong breakers are used with the buss bar, they might snap on and work, but not be able to take the current over time.  Coupled with high humidity, you can start getting corrosion going which further increases the resistance.  Eventually, if its gets bad enough, the resistance can cause glowing red hot metal, and attached insulator plastic starts melting.

Its also possible that someone knocked a wire or breaker loose? Or possibly shorted the buss doing something wrong, corrected the error, but didn't realize the buss had been damaged.    Lots of guessing, but that's how you figure it out.

If it was lightning, there would be lots of related damage: Enphase inverters and other electronics cooked.

Ray Walters
Remote Solar
303 505-8760

On 1/21/20 12:51 PM, Jerry Shafer wrote:
Wrenches
Cant tell anymore but l had a buss failure due to water getting on buss and pealing the tin off the buss and the aluminum base will light up real quick.
Jerry

On Tue, Jan 21, 2020, 9:10 AM Jason Szumlanski <[email protected] <mailto:[email protected]>> wrote:

    (System installed by another contractor...)

    I have been tasked with assisting in the investigation of damage
    in a subpanel used to combine inverter output circuits (5 strings
    of microinverters). There appears to be no damage to conductors or
    other system components. It looks like the damage started at the
    stabs of the bus bar where the breakers connect. Picture attached.
    Here are a few clues:

      * Monitoring indicates that damage occurred overnight a few
        weeks ago. That night we had rain as a winter front came
        through Florida, possibly lightning. The prior day everything
        was fine.
      * The next morning, only 2 of 5 strings started producing power,
        but 4 of 5 strings were reporting data to the Envoy. The two
        strings that were reporting but not producing power reported
        0Vac and Voc on the DC side of the microinverters.
      * A couple of weeks later, 1 of the 2 strings that was producing
        power quit doing so, but continued reporting data.
      * Customer discovered damage yesterday.
      * About a week before the initial damage apparently manifested
        itself, another contractor installed a whole house generator
        transfer switch on the line side of the PV interconnection.
        The generator has never been run (there is not even a LP fuel
        source on site yet). I pointed out that the solar
        interconnection, which was previously on the supply side,
        would need to be moved to the supply side of the generator
        transfer switch's main breaker before operation. During the
        transfer switch installation, the contractor also switched
        line 1 and line 2, but that shouldn't really matter, except
        for Enphase consumption monitoring, which was messed up by the
        swapping of the lines.

    So I'm looking for ideas. I'm wondering if the OCPD would be a
    likely place for lightning damage to manifest itself. I can't
    visually detect any other damage anywhere else. I can't imagine
    that the transfer switch installation would have anything to do
    with it, but the timing is interesting. Other than replacing the
    subpanel and OCPD and firing it back up (no pun intended), I'm not
    sure how to approach further investigation.

    Jason Szumlanski
    Florida Solar Design Group

    *

    *
    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/[email protected]/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to