What made this installation (again, by others) a bit more complicated was
that all branch circuit line conductors were black. I make it a point on my
installations to require black for L1 and red for L2 up to #6 wire size.
It's not a failsafe by any means but does reduce risk.




On Thu, Jan 23, 2020 at 2:41 PM August Goers <[email protected]> wrote:

> Jason -
>
> Thanks for sharing - this is a good lesson for all Wrenches. Years ago we
> had a dual string inverter installation where the DC positives and
> negatives were mixed between the two interters. String 1 positive went to
> inverter 1, string 1 negative went to inverter 2 and vice versa. The
> inverters tested out and ran for about two weeks and then one of them
> literally caught on fire. Since then, we implemented a policy of checking
> wiring coming from the roof down individually. In the case of microinverter
> branch circuits, this means checking each branch circuit voltage on the
> roof with the other breakers off one branch at a time.
>
> Not to get too far off on a tangent, but as we're installing more and more
> energy storage with lots of onsite wiring work, it is clear that fully
> testing wiring is of utmost importance. We have a procedure for checking
> voltage at each piece of equipment (such as a backup loads panel, etc)
> prior to turning on branch breakers. We've run into a couple of
> scenarios where hots and neutrals were mixed up causing 240 v to go to a
> 120 v circuit. Not good.
>
> August
>
> On Wed, Jan 22, 2020 at 2:58 PM Jason Szumlanski <
> [email protected]> wrote:
>
>> I discovered the issue I believe, so I thought I'd update all of you who
>> gave me ideas on what to look for (thank you).
>>
>> And this is something that I stress the importance of all the time...
>>
>> The branch circuit pairs were not properly paired up! All of the L1
>> conductors went to L1 on the bus and all of the L2 to L2. However, for
>> example, circuit 1 L1 and circuit 2 L2 were on a single 2-pole breaker. And
>> circuit 2 L1 and circuit 1 L2 were on another breaker. Everything worked
>> because it was electrically connected to the right bus bar. However, when
>> there was a previous fault one of the breakers probably didn't trip when it
>> should have as a result of the improper pairings. It was reset a few times
>> and just kept heating up and heating up.
>>
>> This isn't conclusive, but it sure makes sense. It wasn't fun tracking
>> this down with 5 strings and 5 junction boxes on the roof, but once we
>> started continuity testing and finding strange results, it became clear.
>>
>> Jason Szumlanski
>>
>>
>>
>> On Tue, Jan 21, 2020 at 12:10 PM Jason Szumlanski <
>> [email protected]> wrote:
>>
>>> (System installed by another contractor...)
>>>
>>> I have been tasked with assisting in the investigation of damage in a
>>> subpanel used to combine inverter output circuits (5 strings of
>>> microinverters). There appears to be no damage to conductors or other
>>> system components. It looks like the damage started at the stabs of the bus
>>> bar where the breakers connect. Picture attached. Here are a few clues:
>>>
>>>    - Monitoring indicates that damage occurred overnight a few weeks
>>>    ago. That night we had rain as a winter front came through Florida,
>>>    possibly lightning. The prior day everything was fine.
>>>    - The next morning, only 2 of 5 strings started producing power, but
>>>    4 of 5 strings were reporting data to the Envoy. The two strings that 
>>> were
>>>    reporting but not producing power reported 0Vac and Voc on the DC side of
>>>    the microinverters.
>>>    - A couple of weeks later, 1 of the 2 strings that was producing
>>>    power quit doing so, but continued reporting data.
>>>    - Customer discovered damage yesterday.
>>>    - About a week before the initial damage apparently manifested
>>>    itself, another contractor installed a whole house generator transfer
>>>    switch on the line side of the PV interconnection. The generator has 
>>> never
>>>    been run (there is not even a LP fuel source on site yet). I pointed out
>>>    that the solar interconnection, which was previously on the supply side,
>>>    would need to be moved to the supply side of the generator transfer
>>>    switch's main breaker before operation. During the transfer switch
>>>    installation, the contractor also switched line 1 and line 2, but that
>>>    shouldn't really matter, except for Enphase consumption monitoring, which
>>>    was messed up by the swapping of the lines.
>>>
>>> So I'm looking for ideas. I'm wondering if the OCPD would be a likely
>>> place for lightning damage to manifest itself. I can't visually detect any
>>> other damage anywhere else. I can't imagine that the transfer switch
>>> installation would have anything to do with it, but the timing is
>>> interesting. Other than replacing the subpanel and OCPD and firing it back
>>> up (no pun intended), I'm not sure how to approach further investigation.
>>>
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>>
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/0630738790020bf17b7774ad6ed4464425204c4b?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=636f6272fa7ddeb8>
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>> <https://mailtrack.io/trace/link/723f771ba6190c7b8fc2fd06f31ea7a6b6ab41c0?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f6676786e8e04410>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/d7ea9ae3eaf8765631db5d80b47f3267e01120c0?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=7b3d598ee513f514>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/01c37be05208c0de420580d892b553f82dfadc19?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=01eb85f151b00d5d>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/36360340e428b3c123126012a4fa231afa4d6f05?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=ed994c188e79c2d3>
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
> <https://mailtrack.io/trace/link/6cd516775bc1800cf14b878dba3290cc3ab86de6?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=1c8f4f1539e9183a>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/9c3fae629a074d4c8ae47e0eaf0c5201471c0b1d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=6fda5140d3ecc484>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/ad276d8b16d068c12a6ea6c0cd4c11cbd1f413a5?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=92016f985d4b96d5>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings: