Is this an off grid system? If so, the generator needs to be running to execute 
EQ on the inverter.

Thank you,

Maverick


> On Jan 31, 2020, at 1:50 PM, Eric Smiley <[email protected]> wrote:
> 
> 
> I recently discovered a critical problem with a client's SW inverter and I 
> want to know if others have encountered this. 
> It's an SW4024 with Flooded Lead Acid batteries. The system is configured 
> using the Custom Battery setting: Bulk and Absorption are set to 29.2 V. 
> Equalize is set to 32 V.
> The problem is when Equalize is enabled, the system goes through Bulk and 
> Absorption just fine. However, when it switches to Equalize it doesn't 
> actually equalize. What I observed was the voltage actually decreased to 0.5 
> V below the Absorption Voltage setting. 
> 
> Eric Smiley, P.Eng.
> Project Manager, North Island
> 
> E:  [email protected]
> T:  1-888-386-0116 ext 702 (toll free)
> C:  250-703-6004
> W:  viridianenergy.ca
> 
> 
> RENEWABLE POWER NOW
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to