What I've noticed is that most of the AIMS inverters are not UL, ETL, or otherwise third-party tested. And none seam to be designed for utility interactive operation.

Kent Osterberg
Blue Mountain Solar


On 2/21/2020 1:37 PM, wes kennedy wrote:
Hi Jeff,

I think the biggest split phase sunny island system is 4 units, so that's 24KW.

What do you do for larger systems? Segment the loads? Not always very practical.

This latest opportunity is for an agricultural building that peaks at 75KW.



-Wes Kennedy 303-653-3073


On Friday, February 21, 2020, 12:47:39 PM MST, Jeff Clearwater <[email protected]> wrote:


All of my SMA Sunny Island Sunny Boy AC coupled systems greater than 12 KW have worked flawlessly and delivered reliable power and good monitoring for years. Less excited about my Schneider and Outback systems due to callbacks and hassles.  a bit more expensive but worth it IMHO.

Hope that helps!

Jeff

wes kennedy wrote on 2/21/20 9:41 AM:
Hi friends,

I keep running across opportunities with 50KW-300KW peak load requirements, on split phase services. Big homes, agriculture etc.

Outback, Schneider, SMA can all gang/stack into the 30-50KW range, but north of there, I am not finding many (any?) options?

Just found Aims Power 50 KW split phase unit with claims of higher power offerings by special order. Even the 50KW unit is $20K, so quite spendy. Any experience with these guys? 50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc TO 220/230/240 Vac <https://www.aimscorp.net/50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html>


        


        


    50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384
    Vdc TO ...

50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc Split Phase 220/230/240

<https://www.aimscorp.net/50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html>


Thanks for any input!

-Wes Kennedy 303-653-3073
on this list since the 90's


_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]  
<mailto:[email protected]>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org  <http://www.members.re-wrenches.org>


--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to