Need to edit this post: The micro inverters are UL listed for grid
connected operation.
What I've noticed is that most of the AIMS inverters are not UL, ETL, or
otherwise third-party tested. And none seam to be designed for utility
interactive operation.
Kent Osterberg
Blue Mountain Solar
On 2/21/2020 1:37 PM, wes kennedy wrote:
Hi Jeff,
I think the biggest split phase sunny island system is 4 units, so
that's 24KW.
What do you do for larger systems? Segment the loads? Not always very
practical.
This latest opportunity is for an agricultural building that peaks at
75KW.
-Wes Kennedy 303-653-3073
On Friday, February 21, 2020, 12:47:39 PM MST, Jeff Clearwater
<[email protected]> wrote:
All of my SMA Sunny Island Sunny Boy AC coupled systems greater than
12 KW have worked flawlessly and delivered reliable power and good
monitoring for years. Less excited about my Schneider and Outback
systems due to callbacks and hassles. a bit more expensive but worth
it IMHO.
Hope that helps!
Jeff
wes kennedy wrote on 2/21/20 9:41 AM:
Hi friends,
I keep running across opportunities with 50KW-300KW peak load
requirements, on split phase services. Big homes, agriculture etc.
Outback, Schneider, SMA can all gang/stack into the 30-50KW range, but
north of there, I am not finding many (any?) options?
Just found Aims Power 50 KW split phase unit with claims of higher
power offerings by special order. Even the 50KW unit is $20K, so quite
spendy. Any experience with these guys?
50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc
TO 220/230/240 Vac
<https://www.aimscorp.net/50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html>
50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384
Vdc TO ...
50kw - 50,000 WATT DC TO AC PURE SINE POWER INVERTER CHARGER 384 Vdc
Split Phase 220/230/240
<https://www.aimscorp.net/50kw-50-000-watt-dc-to-ac-pure-sine-power-inverter-charger-384-vdc.html>
Thanks for any input!
-Wes Kennedy 303-653-3073
on this list since the 90's
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
<mailto:[email protected]>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org>
--
~~~~~~~~~~~
Jeff Clearwater
Village Power Design
linkedin <https://www.linkedin.com/in/jeff-clearwater-0622a312/>
www.villagepowerdesign.com <http://www.villagepowerdesign.com>
cell - 413-559-9763
~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
List sponsored by Redwood Alliance
List Address:[email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org