Hi William

3 questions

Did this system used to work?


The surging is happening even with no loads, just battery charging?

Lastly, did you find a charging/ ac amp size that stopped the surging? With 30 
amps it’s still charging  full rate, if you set it down further does it stop?

Jay

Peltz Power. 



> On Mar 19, 2020, at 12:20 AM, William Miller <[email protected]> wrote:
> 
> 
> Mac:
>  
> I know well what the AC input mode is.  This is the project that had the 
> excessive THD on the voltage waveform (>26%f).  Here is a link to the case 
> study.
>  
> As you can see, we resolved the problem by changing the AC input mode to 
> Backup.  After recent rains started and generator run became necessary, the 
> client started noticing flickering of lights and refrigerator operation was 
> unreliable. We examined the E-Gauge data and could see rapid fluctuations in 
> the generator output.  At one point we saw generator power range from 19kW to 
> 12Kw and back in about 2 seconds.
>  
> We isolated the generator into a load bank and it was rock solid.  We tried 
> lots of things but when we reconnected the generator to the Radians and 
> switched to the Radians to Generator input mode the surging stopped.  
> Unfortunately, the Generator mode causes tons of THD, as noted in the case 
> study.
>  
> So we can’t use Generator because of THD, and we can’t use Backup (or Support 
> or UPS) because in all these modes the generator surges.
>  
> By the way, this is a newish Kohler 30RCL.  This should be a rock-solid match 
> to a 24 kW Radian system.
>  
> Like I said, we tried lots of things.  What stopped the surging was to open 
> the AC input breaker to Inverter 1.  It did not help to open the input to 
> Inverters 2 or 3.  I don’t have a clue as to why this is so…
>  
> We tried taking Inverter 1 out of the system--moving inverter 2 up to Master 
> and Inverter 3 to Slave 1.  The generator still surged. So if anyone started 
> to think Inverter 1 was the problem, this was not confirmed.
>  
> We are certain the neutral bonding is exactly as it should be.  We tripled 
> checked this when chasing the THD problems.  We also adjusted input AC from 
> 30 to 50 (per port), no improvement.
>  
> I must say Outback has been very available to us as we try to figure these 
> problems out.  I am fortunate that I am working with a senior engineer.  We 
> are both currently stumped, but we are going to consult again tomorrow and 
> see if any other ideas come to us.
>  
> Thanks everyone for the input.  More soon.
>  
> William Miller
>  
>  
> From: RE-wrenches [mailto:[email protected]] On 
> Behalf Of Mac Lewis
> Sent: Wednesday, March 18, 2020 6:35 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Generator surging
>  
> Hi William,
>  
> Do you know what your AC input mode is?  
> I'd try playing with this mode.  
> If you have a generator, I'd try switching between "generator", "support".  
> You may quickly see a difference.  There is a small diode symbol that shows 
> up on the Mate3s screen during generator charging.  I don't fully understand 
> what that means but I know that it can affect how a generator works with the 
> Radian.
>  
> Also, you may try lowering the charging current and see how the generator 
> responds.
>  
> What type of generator?  Whats your AC input limits?
>  
> On Wed, Mar 18, 2020 at 6:56 PM Jerry Shafer <[email protected]> wrote:
> Adjust the generator max output in the outback down and see what happens
> Jerry
>  
> On Wed, Mar 18, 2020, 4:04 PM William Miller <[email protected]> wrote:
> Friends:
>  
> I have a 24kW Radian system that is acting up.  The problem is when the 
> generator is running, it surges.  Voltage and power go up and down.  We 
> connected the generator to a load bank and there was no surging.  This makes 
> me think the problem is in the Radian system.
>  
> Has anyone else experienced this?
>  
> Thanks in advance for any input.
>  
> William Miller
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
>  
> --
>  
>  
>  
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to