And also most battery chargers are not multi stage they’re big taper type 
chargers

They don’t charge nearly as efficiently or as well as a three stage inverter 
charger

Bob Ellison

> On Apr 21, 2020, at 12:32 PM, Jason Szumlanski 
> <[email protected]> wrote:
> 
> I'm not sure I follow. I would disconnect the generator AC2 input from the 
> existing quad XW system and move it to the external chargers. Or, I could 
> just turn the charging off by software config in the XWs.
> 
> If I were to buy four inverter/chargers to serve as "external" chargers for 
> the battery (any brand, really) I would just connect the generator input to 
> AC2 and the battery to the batt terminals of the four inverters. The AC1 
> input/output would have no connections. The inverter function would be turned 
> off and the charger function turned on. 
> 
> Again, this would be an expensive solution. I'm sure there are some companies 
> making high output DC chargers. I assume a 48V model will be able to go up to 
> 60V charging output, which would be plenty for my 51V nominal system. 
> 
> 
> 
> 
> 
>> On Tue, Apr 21, 2020 at 11:44 AM Dave Angelini Offgrid Solar 
>> <[email protected]> wrote:
>> 4 xw's need the external relay contactors not the internals, Right?
>> 
>> You will destroy the internals relays. If there was warranty still left, and 
>> there is not on 6048, you would need to scrap them for parts. Xw logs welded 
>> relay warnings and faults for warranty on all xw's.
>> 
>> Dave Angelini Offgrid Solar
>> "we go where powerlines don't"
>> http://members.sti.net/offgridsolar/
>> e-mail  [email protected]
>> text 209 813 0060
>>> On Tue, 21 Apr 2020 08:27:53 -0400, Jason Szumlanski 
>>> <[email protected]> wrote:
>>> 
>>> I actually need 400Adc at 51V nominal of total charge rate. I was hoping to 
>>> use 100Adc chargers for redundancy, or some combination of 2-8 chargers to 
>>> reach the needed current, assuming they can be synced up. I don't think the 
>>> charging algorithm needs to be complicated. We are basically bulk charging 
>>> the LiPOs to 80% with the battery BMS controlling the generator. The 
>>> concept is to get to 80% sometime in the night and solar kicks in during 
>>> the day to reach 100% using 2-stage charging from the XW charge controllers.
>>>  
>>> The problem I have is the quad XW6048s in the system run at a pretty good 
>>> load typically... often over 50%. This is off-grid with generator backup. 
>>> The transfer switches in the XW6048 are causing surges and brownouts when 
>>> the switched loads are high, especially smart dimmers and televisions. I 
>>> need seamless power for this client. My thought is to abandon the internal 
>>> chargers in the XW6048s and just run loads off inverter power full-time. I 
>>> would charge the batteries with external battery chargers. The tricky part 
>>> is how to adjust the charge rate based on load, and also based on solar 
>>> input. I need to limit the net charging current. Of course, I still need 
>>> 400Adc of charging current, which I'm learning might be hard to find. I 
>>> don't really want to buy four more XWs - that's a pretty expensive 
>>> solution. 
>>>  
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>>  
>>> 
>>>> On Fri, Apr 17, 2020 at 4:26 PM Dave Angelini Offgrid Solar 
>>>> <[email protected]> wrote:
>>>> I use the CSW 4048. It has a 50 amp charger. A good spare for clients. Get 
>>>> 2 of them. Repurpose an old Radian or XW well over 100A. XW+ is 140adc.
>>>> 
>>>> Dave Angelini Offgrid Solar
>>>> 
>>>> "we go where powerlines don't"
>>>> http://members.sti.net/offgridsolar/
>>>> e-mail  [email protected]
>>>> text 209 813 0060
>>>> On Fri, 17 Apr 2020 14:21:14 -0400, Jason Szumlanski 
>>>> <[email protected]> wrote:
>>>> 
>>>> I'm looking for a standalone 51V nominal battery charger suitable for a 
>>>> LiPO battery with 2-stage charging and adjustable setpoints for max 
>>>> current and battery voltage. It would require dual chargers with 100A 
>>>> capacity (I want dual chargers for redundancy so I have at least 50% 
>>>> capacity if one goes bad). Ideally they would sync up so they change 
>>>> stages simultaneously, but I'm not sure if that's really important.
>>>>  
>>>> Who makes something like that?
>>>>  
>>>> Jason Szumlanski
>>>>  
>>>>  
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: [email protected]
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: [email protected]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/[email protected]/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to