Marysville Marine can replace XW welded relays.
PJ GONZALEZ <[email protected]>
---
On 2020-04-21 11:44, Dave Angelini Offgrid Solar wrote:
4 xw's need the external relay contactors not the internals, Right?
You will destroy the internals relays. If there was warranty still left, and
there is not on 6048, you would need to scrap them for parts. Xw logs welded
relay warnings and faults for warranty on all xw's.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail [email protected]
text 209 813 0060
On Tue, 21 Apr 2020 08:27:53 -0400, Jason Szumlanski <[email protected]> wrote:
I actually need 400Adc at 51V nominal of total charge rate. I was hoping to use 100Adc chargers for redundancy, or some combination of 2-8 chargers to reach the needed current, assuming they can be synced up. I don't think the charging algorithm needs to be complicated. We are basically bulk charging the LiPOs to 80% with the battery BMS controlling the generator. The concept is to get to 80% sometime in the night and solar kicks in during the day to reach 100% using 2-stage charging from the XW charge controllers.
The problem I have is the quad XW6048s in the system run at a pretty good load typically... often over 50%. This is off-grid with generator backup. The transfer switches in the XW6048 are causing surges and brownouts when the switched loads are high, especially smart dimmers and televisions. I need seamless power for this client. My thought is to abandon the internal chargers in the XW6048s and just run loads off inverter power full-time. I would charge the batteries with external battery chargers. The tricky part is how to adjust the charge rate based on load, and also based on solar input. I need to limit the net charging current. Of course, I still need 400Adc of charging current, which I'm learning might be hard to find. I don't really want to buy four more XWs - that's a pretty expensive solution.
Jason Szumlanski
Florida Solar Design Group
On Fri, Apr 17, 2020 at 4:26 PM Dave Angelini Offgrid Solar <[email protected]> wrote:
I use the CSW 4048. It has a 50 amp charger. A good spare for clients. Get 2 of them. Repurpose an old Radian or XW well over 100A. XW+ is 140adc.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/ [1]
e-mail [email protected]
text 209 813 0060
On Fri, 17 Apr 2020 14:21:14 -0400, Jason Szumlanski <[email protected]> wrote:
I'm looking for a standalone 51V nominal battery charger suitable for a LiPO battery with 2-stage charging and adjustable setpoints for max current and battery voltage. It would require dual chargers with 100A capacity (I want dual chargers for redundancy so I have at least 50% capacity if one goes bad). Ideally they would sync up so they change stages simultaneously, but I'm not sure if that's really important.
Who makes something like that?
Jason Szumlanski
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [2]
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html [3]
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [4]
Check out or update participant bios:
www.members.re-wrenches.org [5]
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm [6]
Check out or update participant bios:
www.members.re-wrenches.org [7]
Links:
------
[1]
https://mailtrack.io/trace/link/818d0fc14d35240172dc7b5e76e9b358639d0699?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&userId=1613865&signature=a20ca8855bc640ef
[2]
https://mailtrack.io/trace/link/47d978507b9775cf89c2c4ac9665997e7f3c2d10?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=61d5cd552bcb7a04
[3]
https://mailtrack.io/trace/link/751a499f55945df4070b9d5521e2cdfbcea242a8?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=8afbf050d5afe9e0
[4]
https://mailtrack.io/trace/link/371ce356d356262bb1fe8e503601758f8bac958e?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=eb4588d3c5c730cd
[5]
https://mailtrack.io/trace/link/e9ea24bb0cec5ce64b3012496a3a8b6390d7a863?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=b340c2774b3cc0f9
[6] http://www.re-wrenches.org/etiquette.htm
[7] http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org