Interesting. I am going to look into that. We are manually stopping the
generator (the BMS kills the two-wire start signal). I don't think the AC2
transfer time matters much in terms of solving the clients complaints, but
I will play with that also.

Thanks!





On Wed, Apr 22, 2020 at 8:18 AM Tump <[email protected]> wrote:

> KISS…. have you checked the low voltage setting on AC2? Make sure that is
> is not set  to the default settings. AC Transfer time? I set to
> the lowest time, I believe its 1.
> You also have 4 inverters what IS the charge setting of these units? "Gen
> assist" enabled?
> Info from Schneider engineer below;
> The AGS will cause XW+ to disconnect the generator when a stop signal is
> sent (Auto Stop) for the generator cool down period (user
> adjustable-AGS>Advanced Settings>Cfg Gen). If you are just manually
> stopping the generator, then it is possible for the XW+ to stay connected
> all the way down to 80V unless you increase that low AC value in
> XW+>Advanced Settings>AC Settings menu. *AC2 transfer time may also be
> adjusted (default is 40s) using Combox, Gateway or Config Tool.   This is
> the time it takes to switch from gen to inverting. *
> Hope that helps,
> Eric
>
> On Apr 21, 2020, at 4:27 PM, Jason Szumlanski <
> [email protected]> wrote:
>
> The issue is during switching only. During inverter operation everything
> is silky smooth. During generator operation things are mostly smooth, but
> large loads that come on or off during heavy charging can cause some
> surging, but that is more a function of a junky generator (which was just
> replaced with a better unit).
>
> So the natural conclusion by the client is let's just run on
> battery/inverter all the time. And it does make sense. And it's his money.
>
>
>
>
> <https://mailtrack.io/trace/link/66033386a2a45137f2b120abb405cca4e927d183?url=http%3A%2F%2Fwww.floridasolardesigngroup.com%2F&userId=1613865&signature=4f411814c62fe532>
> *Jason Szumlanski*
> Principal Solar Designer | Florida Solar Design Group
> (239) 491-8010 (239) 410-4985
> www.FloridaSolarDesignGroup.com
> <https://mailtrack.io/trace/link/820314f28a259bd71c900c3d37295758887d5c04?url=http%3A%2F%2Fwww.FloridaSolarDesignGroup.com&userId=1613865&signature=a8e03312019dcafc>
> [image: Facebook]
> <https://mailtrack.io/trace/link/07e1e531a45de497a46be66e6fd5ef0d301cb2b6?url=https%3A%2F%2Fwww.facebook.com%2Ffloridasolardesigngroup&userId=1613865&signature=8fc87785daeb6626>
>  [image:
> Twitter]
> <https://mailtrack.io/trace/link/650dd5b2dbef8e11b3a7fe576865160d8faa8e0a?url=https%3A%2F%2Ftwitter.com%2FFloridaSolarDG&userId=1613865&signature=8a8fc1a336f4dfb7>
>  [image:
> Youtube]
> <https://mailtrack.io/trace/link/05be406956337ef2c9e2a768972030fdda96636b?url=https%3A%2F%2Fwww.youtube.com%2Fchannel%2FUCjnsYt5r7DNJD3ZnqI10j8g&userId=1613865&signature=238dfb7609b42168>
>
>
>
> On Tue, Apr 21, 2020 at 2:29 PM Ray <[email protected]> wrote:
>
>> Are you sure its just the transfer switching causing problems?  I've seen
>> quite a bit of lights dimming, flickering, and strangeness with XW
>> inverters ( and many others) just in normal operation.  Certain LEDs are
>> particularly sensitive, just another appliance coming on can cause
>> noticeable flicker that bothers some clients.  Our solution was to try
>> different brands of LEDs till we found ones that had less trouble.  I
>> recall the Phillips ones being good, but you would have to test a few to
>> see.
>>
>> Ray Walters
>> Remote Solar
>> 303 505-8760
>>
>> On 4/21/20 12:26 PM, Jason Szumlanski wrote:
>>
>> I have not looked into that, but the problem also exists
>> transferring from inverter to generator. The owner wants "clean" power all
>> the time, and just keeping him on inverter power all the time would be a
>> solution.
>>
>>
>>
>>
>> On Tue, Apr 21, 2020 at 9:35 AM Tump <[email protected]> wrote:
>>
>>> Have you shortened the transfer time from gen to inv, voltage “cut
>>> out"acceptance of the gen in power instead of their 90Vac to say 110V/L ?
>>> Raising the output voltage on the 6848s & gen set for VD/voltage sag issues
>>> under heavy loading? Watch this as sometimes under heavy loading it will
>>> cut the AC input. I use the config tool to address this kind of issue,
>>> gives me a bit more control.
>>>  I have a client that has a large external battery charger similar to a
>>> fork truck unit that he alleges causes "dirty power" while the genset is
>>> supplying power to the charger, w/o charging thru the inverters.
>>> Unfortunately w/ the virus I have yet to confirm.
>>>
>>> On Apr 21, 2020, at 8:27 AM, Jason Szumlanski <
>>> [email protected]> wrote:
>>>
>>> I actually need 400Adc at 51V nominal of total charge rate. I was hoping
>>> to use 100Adc chargers for redundancy, or some combination of 2-8 chargers
>>> to reach the needed current, assuming they can be synced up. I don't think
>>> the charging algorithm needs to be complicated. We are basically bulk
>>> charging the LiPOs to 80% with the battery BMS controlling the generator.
>>> The concept is to get to 80% sometime in the night and solar kicks in
>>> during the day to reach 100% using 2-stage charging from the XW charge
>>> controllers.
>>>
>>> The problem I have is the quad XW6048s in the system run at a pretty
>>> good load typically... often over 50%. This is off-grid with generator
>>> backup. The transfer switches in the XW6048 are causing surges and
>>> brownouts when the switched loads are high, especially smart dimmers and
>>> televisions. I need seamless power for this client. My thought is to
>>> abandon the internal chargers in the XW6048s and just run loads off
>>> inverter power full-time. I would charge the batteries with external
>>> battery chargers. The tricky part is how to adjust the charge rate based on
>>> load, and also based on solar input. I need to limit the net charging
>>> current. Of course, I still need 400Adc of charging current, which I'm
>>> learning might be hard to find. I don't really want to buy four more XWs -
>>> that's a pretty expensive solution.
>>>
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>>
>>>
>>> On Fri, Apr 17, 2020 at 4:26 PM Dave Angelini Offgrid Solar <
>>> [email protected]> wrote:
>>>
>>>> I use the CSW 4048. It has a 50 amp charger. A good spare for clients.
>>>> Get 2 of them. Repurpose an old Radian or XW well over 100A. XW+ is 140adc.
>>>>
>>>> *Dave Angelini Offgrid Solar*
>>>>
>>>> *"we go where powerlines don't"
>>>> http://members.sti.net/offgridsolar/ 
>>>> <https://mailtrack.io/trace/link/290c2833767afa7e7c0b639ab4d233b97fddd564?url=http%3A%2F%2Fmembers.sti.net%2Foffgridsolar%2F&userId=1613865&signature=e52be68029129b4f>
>>>> e-mail  [email protected] <[email protected]>
>>>> text 209 813 0060*
>>>>
>>>> On Fri, 17 Apr 2020 14:21:14 -0400, Jason Szumlanski <
>>>> [email protected]> wrote:
>>>>
>>>> I'm looking for a standalone 51V nominal battery charger suitable for a
>>>> LiPO battery with 2-stage charging and adjustable setpoints for max current
>>>> and battery voltage. It would require dual chargers with 100A capacity (I
>>>> want dual chargers for redundancy so I have at least 50% capacity if one
>>>> goes bad). Ideally they would sync up so they change stages simultaneously,
>>>> but I'm not sure if that's really important.
>>>>
>>>> Who makes something like that?
>>>>
>>>> Jason Szumlanski
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> List Address: [email protected]
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> <https://mailtrack.io/trace/link/2c8383435a52be99ea6f1adaf9dfaa2f1b3fb259?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=59aaebd1c76f9454>
>>>>
>>>> List-Archive:
>>>> http://www.mail-archive.com/[email protected]/maillist.html
>>>> <https://mailtrack.io/trace/link/8f98d67ae7b562b5855cb7cc6f1cb42e11a50a99?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=d07f36493c98b97b>
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> <https://mailtrack.io/trace/link/8f81d3140b61586335b7c5ed188783f0342bc2ab?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=8dd98de73b717e94>
>>>>
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>>> <https://mailtrack.io/trace/link/291c006dfa87eb9a60fdce3f9acfa512e3fc9523?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=05d52193d638afd6>
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/2b9c7e98f244f36f6f97acebbb31fa6f52bb083d?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=766fe3dd1e1f938a>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> <https://mailtrack.io/trace/link/513dffc08f8ebd182e2fc9cd208b1ab5dd5a5329?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=ee7f76ae7d350857>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/a51bdf407e4e0bb98e02e71af34330c35f325698?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=c333baa0c0aa0736>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/d527bd19df5a7006163ddb66e3409cdda563e359?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=f6f4243adaf90546>
>>>
>>>
>>> *[email protected]*               *www.SWNL.net*
>>>                 Solarwinds Northernlights
>>> *       Serving Mid Coast Maine & Northern California*
>>> *                         207-832-7574   Cl.
>>> 610-517-8401                              *
>>>                               *Blair "TUMP" May*
>>>
>>>
>>> *               ********  MAINE'S CHARTER ********  *                   *
>>> NABCEP    "Certified PV Installer"*
>>>
>>>
>>> *                  ********  MAINE'S CHARTER ********           **
>>> Trace Xantrex "Certified" Dealer / Installer"*
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> <https://mailtrack.io/trace/link/b699f67e4c9e3507bd5c739adc3c5256e8eab61e?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c282925db000f213>
>>>
>>> List-Archive:
>>> http://www.mail-archive.com/[email protected]/maillist.html
>>> <https://mailtrack.io/trace/link/500f7759e1ba4092cf35974752b887ea353397eb?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=18ea22ac66c0e187>
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> <https://mailtrack.io/trace/link/a704281366810bdedf8dca9206732ec881b97237?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=598ebb3877e1425b>
>>>
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> <https://mailtrack.io/trace/link/64b50b1f31a2e2ed2c41796cb1e3f872a0c8c3f3?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=e853edec7f4e5783>
>>>
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & 
>> settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>  
>> <https://mailtrack.io/trace/link/10d6d463155f275b52fedff26d22cddd175cf75e?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=fa3e2215a2b180be>
>>
>> List-Archive: 
>> http://www.mail-archive.com/[email protected]/maillist.html 
>> <https://mailtrack.io/trace/link/433140c89638905f48058ed76695feb11780fd94?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=4c161acf68a712f7>
>>
>> List rules & etiquette:www.re-wrenches.org/etiquette.htm 
>> <https://mailtrack.io/trace/link/ba6694855252cb96f47c5cbb640dacf62ff28590?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f4ab19ce4fb08805>
>>
>> Check out or update participant bios:www.members.re-wrenches.org 
>> <https://mailtrack.io/trace/link/d0bc581668f9d9edb45e897931a6b7a24264f028?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=4f5c75021e62fc91>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <https://mailtrack.io/trace/link/94c6c205af838d5c8a00179dd448b37cd493ca4f?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c79e932e7280e377>
>>
>> List-Archive:
>> http://www.mail-archive.com/[email protected]/maillist.html
>> <https://mailtrack.io/trace/link/ff405a5330a5bf63ad8e4d1e282d85a2176301cd?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=6ce95c12b87c5665>
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> <https://mailtrack.io/trace/link/b15bf50b7775f752a12dc98f10c84ef31b3f556b?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=c0606f62e56a2961>
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> <https://mailtrack.io/trace/link/831a26af6eb4aa8f26a4affdc946762acbbeab21?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=db3a284220a0f623>
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/929c119d764128c429afefbc2b8c6aa79080b589?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=c28046f1773b0816>
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
> <https://mailtrack.io/trace/link/e4b652c227c1c6d738e58667d5574202b8e6a6a8?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=3a9b447344ddd63c>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/87b69231252f231980cd831f20505b27ffefc53a?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=57b721191d4d6e0d>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/2d9831d4b94ce6df65cb60a35bc29f23ef3257c1?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=a8cc7d3017723263>
>
>
>
>
> *[email protected]*               *www.SWNL.net*
>                 Solarwinds Northernlights
> *       Serving Mid Coast Maine & Northern California*
> *                         207-832-7574   Cl.
> 610-517-8401                              *
>                               *Blair "TUMP" May*
>
>
> *               ********  MAINE'S CHARTER ******** *                   *
> NABCEP    "Certified PV Installer"*
>
>
> *                 ********  MAINE'S CHARTER ********          **
> Trace Xantrex "Certified" Dealer / Installer"*
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> <https://mailtrack.io/trace/link/6ce64c74070cebafe3c06b49b8212ff7e140fea8?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=02f70045987b6b59>
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
> <https://mailtrack.io/trace/link/e4b652c227c1c6d738e58667d5574202b8e6a6a8?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=3a9b447344ddd63c>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> <https://mailtrack.io/trace/link/87b69231252f231980cd831f20505b27ffefc53a?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=57b721191d4d6e0d>
>
> Check out or update participant bios:
> www.members.re-wrenches.org
> <https://mailtrack.io/trace/link/2d9831d4b94ce6df65cb60a35bc29f23ef3257c1?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=a8cc7d3017723263>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to