Hey Wrenchers,

This is an installation with two Solaredge Storedge 7.6 inverters and the
LG Chem Resu 10 batteries. When the utility goes down the two inverters for
the solar switch over to back up mode and feed two separate dedicated loads
panels. One panel works fine and all of the dedicated loads connected to it
work as normal. Within the other panel there are just two loads, some
lights and some sump pumps that are connected to a controller.

Before the pumps will operate the controller that monitors their operation
also monitors the utility voltage so that the pumps don't see too high or
low of voltage from the utility (or back up power). In normal utility mode
the controller works fine. However when the system switches to backup mode
the controller trips off.

 The voltage window for the pump controller is relatively narrow, however
I'm not sure if that is the problem. The pump(s) will surge to a maximum of
20A at 240V for about a second and then hold between 7A-14A respectively.
Which is within the operating window of the inverter (6600w surge 25A max
continuous).

I connected the controller load to my Eguage and logged the controllers
usage both while connected to the utility and while connected to the
battery back up. The data while connected to the utility is pretty typical
with no irregularities. However when I switch to the battery side my
logging disappears (measuring second by second and the results only show
minutes). I believe that this is due to the inverter shutting down
momentarily and then the Eguage needs to reboot. In all of the starting and
stopping of the inverter I do see that the voltage spikes to L1-149V and
L2-150V together with 299V L1&L2.

Has anyone else encountered this problem before or something similar that
may be able to offer some advice? I had an issue once before and added a
50mf capacitor to the line to smooth out the surge but this was for my home
experiment and not a professional installation. Any luck with power line
conditioners? Thanks in advance,

Jon Siegenthaler
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org