Jones
Solaredge does not like to surge or ramp up quickly, in conversations with
SE the fix might be a variable frequency controller, I do not know how the
controller you have will work but historically that the cure.
Jerry

On Mon, Jun 8, 2020, 8:15 AM Jon Siegenthaler <[email protected]>
wrote:

> Hey Wrenchers,
>
> This is an installation with two Solaredge Storedge 7.6 inverters and the
> LG Chem Resu 10 batteries. When the utility goes down the two inverters for
> the solar switch over to back up mode and feed two separate dedicated loads
> panels. One panel works fine and all of the dedicated loads connected to it
> work as normal. Within the other panel there are just two loads, some
> lights and some sump pumps that are connected to a controller.
>
> Before the pumps will operate the controller that monitors their operation
> also monitors the utility voltage so that the pumps don't see too high or
> low of voltage from the utility (or back up power). In normal utility mode
> the controller works fine. However when the system switches to backup mode
> the controller trips off.
>
>  The voltage window for the pump controller is relatively narrow, however
> I'm not sure if that is the problem. The pump(s) will surge to a maximum of
> 20A at 240V for about a second and then hold between 7A-14A respectively.
> Which is within the operating window of the inverter (6600w surge 25A max
> continuous).
>
> I connected the controller load to my Eguage and logged the controllers
> usage both while connected to the utility and while connected to the
> battery back up. The data while connected to the utility is pretty typical
> with no irregularities. However when I switch to the battery side my
> logging disappears (measuring second by second and the results only show
> minutes). I believe that this is due to the inverter shutting down
> momentarily and then the Eguage needs to reboot. In all of the starting and
> stopping of the inverter I do see that the voltage spikes to L1-149V and
> L2-150V together with 299V L1&L2.
>
> Has anyone else encountered this problem before or something similar that
> may be able to offer some advice? I had an issue once before and added a
> 50mf capacitor to the line to smooth out the surge but this was for my home
> experiment and not a professional installation. Any luck with power line
> conditioners? Thanks in advance,
>
> Jon Siegenthaler
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/[email protected]/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to