Hi Jon, 

I have zero experience with the LG RESU 10H hi voltage
battery. I assume resu10H is what you mean and not resu10? 

That said I
did alot of testing with Schneider and LG for their attempt to make a 48V
resu10 NMC offgrid system in 2017. 

Schneider had to derate XW+ to less
than it's full output to try and make LG Chem happy. In the end the project
ended and not much was said by either party. My input only is that
Solaredge is probably trying to protect the battery from the pump surge.
There is a heartbeat signal that the BMS needs from inverter to keep the
battery on. (major bad design for offgrid, my opinion.) No one does this
now as it is all internal to the battery. Even closed loop systems do not
use this heavy handed design approach. Much better ways these days to do
this reliably. 

The hi voltage you see, is it possible it is the unloading
of the inverter after a surge? I guess it would be hard to reverse the load
panels to test? Will think about this later some more. Good Luck!  

Dave
Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail [email protected]
[2]
text 209 813 0060

On Mon, 8 Jun 2020 10:14:46 -0500, Jon Siegenthaler 
wrote:   Hey Wrenchers,   This is an installation with two Solaredge
Storedge 7.6 inverters and the LG Chem Resu 10 batteries. When the utility
goes down the two inverters for the solar switch over to back up mode and
feed two separate dedicated loads panels. One panel works fine and all of
the dedicated loads connected to it work as normal. Within the other panel
there are just two loads, some lights and some sump pumps that are
connected to a controller.    Before the pumps will operate the controller
that monitors their operation also monitors the utility voltage so that the
pumps don't see too high or low of voltage from the utility (or back up
power). In normal utility mode the controller works fine. However when the
system switches to backup mode the controller trips off.      The voltage
window for the pump controller is relatively narrow, however I'm not sure
if that is the problem. The pump(s) will surge to a maximum of 20A at 240V
for about a second and then hold between 7A-14A respectively. Which is
within the operating window of the inverter (6600w surge 25A max
continuous).    I connected the controller load to my Eguage and logged the
controllers usage both while connected to the utility and while connected
to the battery back up. The data while connected to the utility is pretty
typical with no irregularities. However when I switch to the battery side
my logging disappears (measuring second by second and the results only show
minutes). I believe that this is due to the inverter shutting down
momentarily and then the Eguage needs to reboot. In all of the starting and
stopping of the inverter I do see that the voltage spikes to L1-149V and
L2-150V together with 299V L1">   Has anyone else encountered this problem
before or something similar that may be able to offer some advice? I had an
issue once before and added a 50mf capacitor to the line to smooth out the
surge but this was for my home experiment and not a professional
installation. Any luck with power line conditioners? Thanks in advance,  
Jon Siegenthaler  

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:[email protected]
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to