I take it he will not allow you to tape the wiring with white tape and
put a warning sign on the JB? You have to do what he wants but I feel your
pain. Good Luck! I would think a good electrician would measure first:) 


Dave Angelini Offgrid Solar
"we go where powerlines
don't"
http://members.sti.net/offgridsolar/ [1]
e-mail [email protected]
[2]
text 209 813 0060

On Fri, 12 Jun 2020 15:17:19 -0500, James Jarvis 
wrote:  Hello Wrenches,   I have an off-grid install where I was recently
red-tagged by the state inspector. System is 24 volt with battery, Magnum
inverters, some Magnum charge controllers, and a Morningstar charge
controller. It is permitted under NEC 2017.   One of the inspectors issues
was that my DC- conductors to the array / rapid shut down box are black
color. He wants them to be white because he says they are solidly grounded.
I reason that they are only solidly grounded when they are solidly
grounded. As soon as the ground fault protection breaker opens, they are
floating at array voltage. I think it is misleading and unsafe to have a
white conductor that can have hundreds of volts of potential on it when a
breaker trips.   I haven't dug into the code yet. I'm just working on the
logic that one of my mentors put into me which is white wires better not
have voltage potential on them. "That's the sort of sh*t that kills
electricians" is what he repeatedly said ... and it's stuck with me.  
Thoughts? I'm backed into the corner with the state, so I will be changing
them to white even if it is unsafe ... unless I have some code backing.   
Changing the wires to white will get interesting up on the roof. I wonder
if they want me to cut off the black MC on the modules and replace them
with white? This is mostly just an exercise in the State of Minnesota only
wanting to know about and allow micro inverters. They brought in a state
inspector from three hours away who kept repeating that he was a "highly
qualified individual", but was unable to identify or recognize a charge
controller. He kept referring to the charge controllers as inverters.  
Thanks, 
    -James Jarvis
APRS World, LLC
+1-507-454-2727
http://www.aprsworld.com/ [3]     

Links:
------
[1]
http://members.sti.net/offgridsolar/
[2] mailto:[email protected]
[3]
http://www.aprsworld.com/
_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to