It relates specifically to Simpliphi, but all brands of Li+ need much higher LBCO set points compared to Lead acid. Hysteresis and time don't fix the fact that once the batteries shut off before the inverter, the entire system is inoperable, with no charging available from the PV.  It creates an absolute failure, that requires a manual reset, and there is no reason for it.  It should be an easy firmware fix to allow LBCO to go above 48.  We've used other brands of inverters and had excellent results with extremely high efficiency charging, noticeably reduced gen run time, etc. We can set the autostart on the generator to start higher, but as soon as there is a problem with the generator, we're snow shoeing in to save the house.  Already done it 3 times this past Winter, so no, this is not a hypothetical problem.

Also, I haven't mentioned Schneider's abysmal tech support throughout this problem.  Zero on site phone support, but we might get a call back a week later, and then the tech can only read from the manual: something we've already done. I dropped Schneider many years ago when they brought out the terrible TR line of inverters. Those had 100% customer dissatisfaction.  They have yet to regain my support, and now after this latest experience, I have to refuse to even service systems with Schneider equipment.

Ray Walters
Remote Solar
303 505-8760

On 8/10/20 8:03 AM, Dave Angelini Offgrid Solar wrote:

Hey Ray,

Your comment on Schneider LBCO relates to which brand? Sympliyfi? Curious because I will send this in again. I did last time and they said to make sure the config person knows that you can also set the default LBCO hysteresis from 2V to 10V and the LBCO time from 60 seconds up to 600 seconds.

Zero probes here for me with Discover AES and Fortress with Schneider electronics.

*Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail [email protected] <mailto:[email protected]> text 209 813 0060*

On Sun, 9 Aug 2020 18:47:50 -0600, Ray <[email protected]> wrote:

My favorite right now is Simpliphi: company has been around since 2002, and as the name implies, they are simple to install.  There is no external monitoring or comm, just an output breaker on each battery that can be reset if the internal BMS ever shuts down for any reason.  We've done several sets in new systems, and as battery replacements with older Outback equipment.  Simpliphi provides a nice programming cheat sheet for all the brands of inverters and charge controllers.

For smaller systems, the LiFe Blue batteries are great.  They have the best monitoring (simple blue tooth to a free phone app)  and they are the only Li+ battery that has a solution for cold weather charging that I'm aware of.  Other battery companies have just given us the shoulder shrug and tell us to install the battery in a conditioned space.  Not a good answer for many off grid systems in the mountains.

I'm not a huge fan of Blue Planet; if their battery is over discharged, it requires a 48 v dark start.  I also did not find their enclosure to be NEC code compliant to connect conduit to.  We had to modify it to allow a 2" KO. Cable routing and connections internally are also awkward. Its just a computer rack cabinet repurposed for batteries, but it does have pretty blue Lights (which we disconnected at the customer's request)  Finally the comm system is based on the E-gage, which was never designed for off grid and depends on a constant router and internet connection to monitor.  That is another deal killer for some remote projects.  Internet connectivity is great when available, just the monitoring can't be dependent on that connection.  Their tech support was good though.

Beware that Schneider inverters LBCO can't be programmed over 48v, which is a deal killer for most Li+ batteries.  We currently have a system that we are adding a relay to shut off AC output, that will be triggered by the charge controller. That is just an amazingly kludgy solution for a really dumb problem: not allowing higher settings of the LBCO.  Until Schneider releases a firmware update, they are not even being considered for future projects.

Ray Walters
Remote Solar
303 505-8760
On 8/9/20 5:30 PM, Jerry Shafer wrote:
I have outback FX systems operating for years now, the lab l had used FX's and midnite systems, it does need to be 48 volts nominal.
Jerry

On Sun, Aug 9, 2020, 4:13 PM Kirk Herander <[email protected] <mailto:[email protected]>> wrote:

    For some reason (that I never got an answer to from Outback or
    Blue Planet) older FX inverters are not compatible with Blue Ion
    LFP batteries. The newer FXR series are.
    Considering one only needs to change slightly charge voltages,
    duration, etc. to meet BI recommendations, it's a mystery why
    Outback states that older FX inverters are not compatible.
    Outback  states this in a tech note about using LI batteries.

        On 8/9/2020 5:40:39 PM, [email protected]
        <mailto:[email protected]>
        <[email protected]
        <mailto:[email protected]>> wrote:

        P.S. The system consists of an old Outback FX inverter and
        an MX60, with
        a 2600 W array.

        ---


        On 2020-08-09 13:12, [email protected]
        <mailto:[email protected]> wrote:
        > Hello Wrenches,
        >
        > What is the best Li-Ion battery to use with an off grid
        system?
        >
        > Thanks,
        >
        > Drake
        > Athens Electric
        >
        > --
        > _______________________________________________
        > List sponsored by Redwood Alliance
        >
        > List Address: [email protected]
        <mailto:[email protected]>
        >
        > Change listserver email address & settings:
        >
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        >
        > List-Archive:
        >
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        >
        > List rules & etiquette:
        > www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>
        >
        > Check out or update participant bios:
        > www.members.re-wrenches.org
        <http://www.members.re-wrenches.org>
        _______________________________________________
        List sponsored by Redwood Alliance

        List Address: [email protected]
        <mailto:[email protected]>

        Change listserver email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org


        List-Archive:
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org


        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out or update participant bios:
        www.members.re-wrenches.org
        <http://www.members.re-wrenches.org>

    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: [email protected]
    <mailto:[email protected]>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>


_______________________________________________
List sponsored by Redwood Alliance

List Address:[email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to