Hey Bill,
   They're still small enough that, at least so far, there is no hold music!
And we combine ac outputs with an "ac combiner panel" simply a single
phase or three phase panel, with each inverter feeding a breaker in that
panel and ensuring that we use either a main breaker that can be back fed
or a panel with feed through lugs. It is simple and safe and code
compliant.


Daryl





> OK, I'll bite.  I use SMA and Outback almost exclusively.  SMA for
> grid-tie so I can't vouch for SI for Off-grid and I don't seem to have
> the same wait problem with SMA, its usually 10-20 minutes.
>
>              And Outback.... well they're not perfect but I've been
> using there stuff since day 1 (thanks Bob-O), still using FX3524 ser#
> 0007 and been installing since they were Trace. Service?  well, let's
> just say it varies but I've been willing to put up with it.  The WORST
> part of of Outback service calls is the music they pipe in on
> 'hold'...its enough to make you hang up.
>
>              Sol-ark, the new kid on the block sounds slick and I'm
> genuinely tempted, specs look great..wonder what their 'hold' music is
> like?
>
> Bill
>
> Feather River Solar Electric
> Bill Battagin, Owner
> 4291 Nelson St.
> Taylorsville, CA 95983
> 530.284.7849
> CA Lic 874049
> www.frenergy.net
>
> On 9/9/2020 6:49 PM, Mark Frye wrote:
>>
>> The most important thing here is that no one is standing up to sing
>> the praises of either SMA or Outback.
>>
>> I myself have sent about 2 hours on hold over 2 days trying to get an
>> issue addressed by SMA.
>>
>> Re: Sol-Arc I would pay a lot extra or take some not so good aspect in
>> exchange for good technical support.
>>
>> On 9/9/2020 1:12 PM, Jason Szumlanski wrote:
>>> Any tips on combining AC output from these units when stacking
>>> several of them? What bus/OCPD system are you using? Same question
>>> for generator/grid input.
>>>
>>> The solar MPPT inputs appear to be dead simple.
>>>
>>> Jason Szumlanski
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>
>
>
> --
> This email has been checked for viruses by Avast antivirus software.
> https://www.avast.com/antivirus
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to